In most cases, you can use either. Whether you should use one versus the other depends on several details. Some out of necessity, some out of preference. Let's start with the building service voltage: 480, 240, or 208 volts? Next, array size?Good morning, we are adding a solar array on the roof of a structure. Question is can we use a single phase residential panel? Or does it have to be a 3 phase panel? Thanks
I (mostly) agree with the avoidance of connecting to the high leg (though I have done it when the transformer driving it was of sufficient capacity), but why would you say not to connect to the center tap?I would say in general there would be two connections to avoid: one is to the open leg of an open delta, and the other is to the center tap of a high leg delta. I would also check with the utility. There is a good chance they will have requirements and restrictions on this.
Good morning, we are adding a solar array on the roof of a structure. Question is can we use a single phase residential panel? Or does it have to be a 3 phase panel? Thanks
Phase balancing is a good point.A lot of utilities require you to balance your system among all the phases, if you use single phase inverters. Some do not even allow single phase inverters on a three phase grid in the first place.
Phase balancing is a good point.
Have any of you ever run into a phase balance requirement when the delivery is via 'unbalanced' open delta?
I (mostly) agree with the avoidance of connecting to the high leg (though I have done it when the transformer driving it was of sufficient capacity), but why would you say not to connect to the center tap?
Then I agree. With a high leg service you can either connect all three phases ungrounded if your inverter(s) can do it and your high leg transformer will take 1/3 the power output, or you can connect single phase to A, C, and neutral. And of course, the governing AHJ has the final word.I meant connecting to the center tap and the high leg. Using the center tap as a neutral/reference is fine.
I would think that depends on the relative transformer sizes and whether it is an open or closed delta.Then I agree. With a high leg service you can either connect all three phases ungrounded if your inverter(s) can do it and your high leg transformer will take 1/3 the power output, or you can connect single phase to A, C, and neutral. And of course, the governing AHJ has the final word.
How so?In the case of an open delta, the high leg "stinger" pot would end up handling more than 1/3 of the generated power.
I see two likely cases for high leg:Does the same issue not affect a load? Can the size of the high-leg service conductor not be a clue? Do I have to limit the inverter output per leg to half of the high-leg service conductor ampacity?
FWIW, I've only ever connected single phase to a high-leg.
Need to know the service details...This installation is going to have 2 single phase 7kw inverters. Balancing as best as possible has come up as an idea but in the end are we going to need to change to 3 phase inverters?
This installation is going to have 2 single phase 7kw inverters. Balancing as best as possible has come up as an idea but in the end are we going to need to change to 3 phase inverters?
This installation is going to have 2 single phase 7kw inverters. Balancing as best as possible has come up as an idea but in the end are we going to need to change to 3 phase inverters?