    Plug & Play Solar kits

    https://cleantechnica.com/2014/03/14...kit-truly-diy/

    I've come across this website for a plug solar panel kit, any code reference that these equipment must comply?

    #2
    Originally posted by HecThor View Post
    https://cleantechnica.com/2014/03/14...kit-truly-diy/

    I've come across this website for a plug solar panel kit, any code reference that these equipment must comply?
    Don't do it. They are just wrong in so many ways.

    Comment


      #3
      Originally posted by HecThor View Post
      https://cleantechnica.com/2014/03/14...kit-truly-diy/

      I've come across this website for a plug solar panel kit, any code reference that these equipment must comply?
      If they are 'installed' they need comply with 690 and 705, to begin with, and they don't. You can be sure the equipment is not UL listed either.

      Comment


        #4
        Originally posted by ggunn View Post
        Don't do it. They are just wrong in so many ways.
        I agree

        Comment


          #5
          Originally posted by jaggedben View Post
          If they are 'installed' they need comply with 690 and 705, to begin with, and they don't. You can be sure the equipment is not UL listed either.
          Haha, exactly "they don't"

          Comment


            #6
            Thanks for that link. The comments were a good read.

            Comment


              #7
              So far I have seen only one "plug-in" solar solution that was actually NEC compliant. It used a non-standard socket on a dedicated circuit which had to be installed for the purpose by an electrician (who was therefore responsible for permit, inspection, 120% rule compliance, etc.)
              Once the receptacle was in place, the homeowner could then plug in the packaged system which he dropped in place (considered a UL-approved product, so arguably no permit required for that part of the installation) to that receptacle. The non-standard plug connector was part of the panel and inverter package.

              Comment


                #8
                from the site comments>>>>>

                The inverters and panels for all of our grid-tie kits are UL-1741 approved,
                &&&&

                The inverter is manufactured in China, and the manufacturer name is Beijing Kinglong New Energy, KLNE series, and model name Sunteams.
                Approval for the method of connection is left to the utility companies. In many states, the AC male plug connection has been approved. In a couple states, it has not been approved, and the kit must be connected directly to the electrical box, adding one more step to the connection process.

                ~RJ~

                Comment


                  #9
                  I guess there are only a 'couple states' that don't follow some version of the NEC.

                  This is a scam, and a potentially dangerous one if a customer pushed the limits.

                  Comment


                    #10
                    Originally posted by GoldDigger View Post
                    ...
                    Once the receptacle was in place, the homeowner could then plug in the packaged system which he dropped in place (considered a UL-approved product, so arguably no permit required for that part of the installation) to that receptacle. The non-standard plug connector was part of the panel and inverter package.
                    It is hardly the case that UL approved equipment doesn't require a permit to install.

                    Comment


                      #11
                      Originally posted by jaggedben View Post
                      It is hardly the case that UL approved equipment doesn't require a permit to install.
                      True, but it might make a permit for owner installation easier to get.

                      Sent from my XT1585 using Tapatalk

                      Comment


                        #12
                        Originally posted by jaggedben View Post
                        It is hardly the case that UL approved equipment doesn't require a permit to install.
                        So, my cord-and-plug connected window AC unit needs a permit?!?

                        The panel system GoldDigger describes is just a difference in scale, not in kind.

                        Comment


                          #13
                          Originally posted by gadfly56 View Post
                          So, my cord-and-plug connected window AC unit needs a permit?!?
                          It might, legally. Ask your local building inspector. But only ask 'hypothetically' or 'for a friend.'

                          The reason it's a scam is that 1) they are exaggerating the acceptance of AHJs and utiliities to the point of being misleading, and 2) they are leaving out that, even if equipment is fine with the authorities, the utilities will still want a passed building permit to give you credits and 3) lacking credits, it's far, far less likely the thing will pay itself back.

                          Also if you look at the website it appears they are not really that serious about the plugged solar thing and are really just trying to resell standard equipment that doesn't give a DYIer any real advantage.

                          Comment


                            #14
                            It does state all components are UL approved -- that doesn't mean the are approved as a package deal --- you can build a luminaire out of UL approved equipment doesn't mean it can be legally installed -- Still has to abide with NEC 690 IMO as a min
                            CircuitRyder --- Unfortunately not all good ideas are code enforceable.

                            Comment


                              #15
                              I have been in many discussions about these things on this and other forums. They are not compliant with the NEC and UL, they are not approved by any AHJ that I know of, and they are potentially dangerous.

                              Comment