Hi,
I am getting a little confused on my transformer sizing and was wondering if I could get some input.
I am looking at 3 inverters output current total equals 240A at 480V.
240 X 1.25 = 300A at 480V
Do I need to size the transformer with taking into account the 1.25 multiplier for continuous load? If so I think I need a 250kva or next size up would be 300kva for 3 phase. If not, and I take the 240A, I think I would need a 200kva or next size up 225kva.
According to my calculations a 225kva has a current rating of 270A on the 480V side.
(225,000/(480x1.732)=270.6A
If my max output total is 240A why wouldn't I be able to use a 225kva?
Next is primary side (utility) OCPD.
Would I use this calculation (ohms law):
300A X 480V = 144,000W
144,000W / 208V = 692A
USE 700A OCPD on primary side?
I feel like I am getting a little lost in my numbers. Appreciate the help!
I am getting a little confused on my transformer sizing and was wondering if I could get some input.
I am looking at 3 inverters output current total equals 240A at 480V.
240 X 1.25 = 300A at 480V
Do I need to size the transformer with taking into account the 1.25 multiplier for continuous load? If so I think I need a 250kva or next size up would be 300kva for 3 phase. If not, and I take the 240A, I think I would need a 200kva or next size up 225kva.
According to my calculations a 225kva has a current rating of 270A on the 480V side.
(225,000/(480x1.732)=270.6A
If my max output total is 240A why wouldn't I be able to use a 225kva?
Next is primary side (utility) OCPD.
Would I use this calculation (ohms law):
300A X 480V = 144,000W
144,000W / 208V = 692A
USE 700A OCPD on primary side?
I feel like I am getting a little lost in my numbers. Appreciate the help!