Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows tap from utility CT to trough to PV disconnect in electrical room inside basement. However from PV disconnect goes straight to roof to switchboard named solar load. From switchboard feeder breaker goes to inverter on roof to strings and modules.

My question is does code require disconnect between PV disconnect and solar load switchboard outside building?
ebbe9286fb6b014db1492a596b0d13b1.jpg


Sent from my SM-G935U using Tapatalk
 

baserunner4

Member
Location
CA
Most requirements for the exact PV disco. location are set forth by the utility. I believe the code mentions a means of disconnect to be in a readily accessible area which includes a locked door in some instances. I rarely see a tie in at the utility ct cabinet. Most utilities are against this. They want a clear distinction between utility and customer/solar.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
In my case the utility service is underground into building basement electric room trough amd the inverter and solar panels are on roof.

Tap from CT is second issue but first issue is I am confused between NEC 2014 695.15(A)(2) and 695.15(A)(3) one says ac disco within sight of inverter which is the solar load switchboard on roof on sketch and other say additional ac disco need to be per 690.13(A) which could be pv system disco in the sketch? Not sure what the code means by an additional disco 695.15(A)(3)?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I'd have to review those sections to be clear which is which. But if I recall correctly, when your inverter is not readily accessible you need to have one disconnect within sight of the inverter and another one that is readily accessible. (Strictly speaking, there can be just one if it is both within sight and readily accessible, but that's not typically possible.)

So yes, your main PV disconnect at the service is your 'additional' one. It can also meet the requirements of 705. If the utility makes you put in another external one then that one can meet all those requirements.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
In my case the utility service is underground into building basement electric room trough amd the inverter and solar panels are on roof.

Tap from CT is second issue but first issue is I am confused between NEC 2014 690.15(A)(2) and 690.15(A)(3) one says ac disco within sight of inverter which is the solar load switchboard on roof on sketch and other say additional ac disco need to be per 690.13(A) which could be pv system disco in the sketch? Not sure what the code means by an additional disco 690.15(A)(3)?

Edit:

Sent from my SM-G935U using Tapatalk
 