    Can i do this

    Attached sketch has AC PV disco and Building Service Disco.

    The GEC from Building Service Disco go to building electrode system. The GEC from AC PV disco gets bonded to the building service disco GEC.

    Is the sketch allowable per NEC 2014?

    Sent from my SM-G935U using Tapatalk

    #2
    Your picture is upside down.
    If you aim at nothing, you will hit it every time!

    Comment


      #3
      Ask your AHJ. This stuff will remain very open to interpretation and preference until you get on the 2020 NEC.

      Comment


        #4
        Attached sketch not upside down.

        AHJ is mute about this matter. Any thoughts, experience or opinions appreciated including what 2020 has to say post #1.

        Question is can I bond AC solar disco GEC with the GEC of building service disco as shown in sketch?



        Sent from my SM-G935U using Tapatalk
        Last edited by hhsting; 04-30-19, 11:41 PM.

        Comment


          #5
          At first sniff i'm inclined towards all GEC's in any given structure bonded together

          ~RJ~

          Comment


            #6
            2020 I believe is going to prohibit a N-G bond in the solar disco and require a supply side bonding jumper back to the main disco. It changed between the first and second draft.

            But I would say that under 2014 and any other code besides 2020, you can treat them like you would multiple service disconnects, if the AHJ doesn't have an opinion.

            Comment


              #7
              Best practices dictate a N-G bond only at one location, the main service disconnect. While we design and treat the solar disconnect as a service disconnect, it's not considered a "service".

              Bond the solar EGC to the main service EGC at the service entrance but leave neutral unbonded in the PV disconnect.

              Comment


                #8
                Originally posted by BandGap1.1eV View Post
                Best practices dictate a N-G bond only at one location, the main service disconnect. While we design and treat the solar disconnect as a service disconnect, it's not considered a "service".

                Bond the solar EGC to the main service EGC at the service entrance but leave neutral unbonded in the PV disconnect.
                You are saying something like the attached sketch?

                Sent from my SM-G935U using Tapatalk

                Comment


                  #9
                  Originally posted by jaggedben View Post
                  2020 I believe is going to prohibit a N-G bond in the solar disco and require a supply side bonding jumper back to the main disco. It changed between the first and second draft.

                  But I would say that under 2014 and any other code besides 2020, you can treat them like you would multiple service disconnects, if the AHJ doesn't have an opinion.
                  Whwre can I find the latest 2020 draft?

                  Sent from my SM-G935U using Tapatalk

                  Comment


                    #10
                    Originally posted by hhsting View Post
                    Whwre can I find the latest 2020 draft?

                    Sent from my SM-G935U using Tapatalk
                    The NFPA website.

                    Roger
                    Moderator

                    Comment


                      #11
                      Originally posted by jaggedben View Post
                      2020 I believe is going to prohibit a N-G bond in the solar disco and require a supply side bonding jumper back to the main disco. It changed between the first and second draft.

                      But I would say that under 2014 and any other code besides 2020, you can treat them like you would multiple service disconnects, if the AHJ doesn't have an opinion.
                      Originally posted by BandGap1.1eV View Post
                      Best practices dictate a N-G bond only at one location, the main service disconnect. While we design and treat the solar disconnect as a service disconnect, it's not considered a "service".

                      Bond the solar EGC to the main service EGC at the service entrance but leave neutral unbonded in the PV disconnect.
                      I'll guess this is the 705/230 quagmire we've been hearing about

                      ~RJ~

                      Comment


                        #12
                        Originally posted by romex jockey View Post
                        I'll guess this is the 705/230 quagmire we've been hearing about

                        ~RJ~
                        They just can't seem to get it right. I thought the first draft was basically fine. And then just when they finally decided to clarify things in 705, the other CMP went ahead and changed 230.71 and created new confusion.

                        Comment


                          #13
                          I still was not able to find 2020 second draft found first draft though.

                          What is the proabability that second draft would be modified into something different i.e third draft? Can they still do that?

                          Sent from my SM-G935U using Tapatalk

                          Comment


                            #14
                            The second draft should be further down the page.

                            2nd draft will not change in substance, only to fix errors.

                            Comment


                              #15
                              Originally posted by jaggedben View Post
                              The second draft should be further down the page.

                              2nd draft will not change in substance, only to fix errors.
                              Is it made public? You have link?

                              Sent from my SM-G935U using Tapatalk

                              Comment