    PV conductors run in attic


    Under 2011 code 690.31(E)(1) stated that wiring methods beneath a roof shall not be installed within 10in of roof deck…

    I can’t find any such code in the 2017 version. Has the implementation of 690.12 and rapid shut down systems deemed the 10in rule no longer a concern?


    Any clarification appreciated.



    #2
    I think you are right that it's gone. I don't know the reason.

    Comment


      #3
      I'm aware of the rule that says you have to make sure your wiring under a roof deck needs to be out-of-the-way of any roofing nails that might be installed later... but 10" seems excessive.

      Comment


        #4
        Originally posted by PaulMmn View Post
        I'm aware of the rule that says you have to make sure your wiring under a roof deck needs to be out-of-the-way of any roofing nails that might be installed later... but 10" seems excessive.
        It was to allow firefighters to safely axe through a roof without fear or cutting into a 600VDC wire from roof mounted PV. Hence my wondering if the introduction of rapid shut down did away with this code.

        Comment


          #5
          The purpose was to protect firefighters and that was taken over by rapid shutdown so it was removed.

          Comment


            #6
            Is it acceptable to run PV DC in FMC in an attic?

            Comment


              #7
              Originally posted by five.five-six View Post
              Is it acceptable to run PV DC in FMC in an attic?
              Yes. 10 inches below the roofdeck under the 2014 NEC.

              Comment