I wanted to share a solar distribution setup I saw at a remote telemetry station and wanted to hear your thoughts. This telemetry station consists of a 48V solar panel feeding a charge controller which feeds a string of battery totaling 48Volts. There is a second load charger which "transfers" the energy from the same battery to the DC load. Both chargers are from the same vendor - Morningstar. I was wandering why they would use two battery chargers, instead of one battery charger and one power supply. I'd think a 48Vdc-48Vdc power supply would provide stable voltage for the load and filter out any "irregularities" on the input.

Thoughts?

Thanks,
EE
 
Initial thought is the second controller could be:

1. A DC DC converter to change or stabilize the battery voltage (48v bank will be between 46 and 60 volts)

2. An inverter.

3. Some sort of load manager/controller.

4. A diversion charge controller where the first controller is used for it's mppt and/or DC DC converter capabilities and not charge control (seems unlikely from your description).

But I don't believe Morningstar makes anything for numbers 1-3, so I think we are back to JB's response ;)
 

pv_n00b

Senior Member
Location
CA, USA
I would say the "load charger"is not a charger but either a DC power supply or an AC inverter. Morningstar does make an inverter.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
The TS45 has a diversion feature so that's almost certainly what it's being used for.

The MPPT-60 will be better at harvesting energy from the array, because its MPPT, but it does not appear to have a diversion feature.

So someone wanted to utilize a diversion load when batteries were full but didn't want to compromise on energy harvest, and spent extra money to get both features.

I think we figured this out. :D
 
.... unless it's being used as a load controller. those TS controllers are able to do 3 modes, one of them being load control. I don't know offhand how the load control functionality is used. You could download the manual and read about it.
 

BillK-AZ

Senior Member
Location
Mesa Arizona
Many telecommunications systems use a -48V (positive is grounded), but the Morningstar controllers are for a negative ground system. It is possible to isolate the array and controller and then ground the battery negative. This works for the charge function, but not for the load if a low voltage disconnect is needed. A work around is often a second controller and a relay for load control. The second controller does not need MPPT.
 