You clearly need to get someone who knows about solar involved in your setup. With a 20 amp service you cannot back fed the panel with 125 amps--The max back fed breaker allowed is 40 amps on a 200 amp panel with a 200 amp ocdp .
Unfortunately this is not a diy site and I must close this thread
Looks like you completely missed the sentence where OP explained a line side tie in was planned DOOOHHH. In that case, the distribution bus bar rating has absolutely nothing to do with it.