    Hello, Everyone!

    We have a customer that is running 24vdc and RS-485 communications lines in the same conduit for a solar PV monitoring application. The questions is wheather the 24vdc needs to be grounded in this application? I have searched quite a bit and can't seem to find any best practices published on this topic. Does anyone have any thoughts on this? Much appreciated!!

    Sean

    #2
    Originally posted by seand27 View Post
    Hello, Everyone!

    We have a customer that is running 24vdc and RS-485 communications lines in the same conduit for a solar PV monitoring application. The questions is wheather the 24vdc needs to be grounded in this application? I have searched quite a bit and can't seem to find any best practices published on this topic. Does anyone have any thoughts on this? Much appreciated!!

    Sean
    is the 24VDC a class 2 circuit?
    Bob

    Comment


      #3
      Hi, Bob.

      Thank you so much for posting a response so quickly. Honestly, I am not sure if it is a Class 2 circuit or not, but I will try and confirm that. The device generating the 24vdc in this case is this Weidmuller power supply:

      https://catalog.weidmueller.com/cata...tID=8739140000

      If this is a class 2 circuit, should the 24VDC be grounded?

      Cheers!
      Sean

      Comment


        #4
        Originally posted by seand27 View Post
        Hi, Bob.

        Thank you so much for posting a response so quickly. Honestly, I am not sure if it is a Class 2 circuit or not, but I will try and confirm that. The device generating the 24vdc in this case is this Weidmuller power supply:

        https://catalog.weidmueller.com/cata...tID=8739140000

        If this is a class 2 circuit, should the 24VDC be grounded?

        Cheers!
        Sean
        The power supply label that you linked to shows it is a listed class 2 power supply so it probably is a class 2 circuit. And equipment grounding conductor is not likely required. I am not real sure if you are asking if an equipment grounding conductor is required or if one leg needs to be grounded.
        Bob

        Comment


          #5
          Great. Thanks Bob.

          So, just so I am clear, does that mean we do not need to ground the 24VDC?

          Thanks!
          Sean

          Comment


            #6
            There is no requirement in the NEC to ground one of the legs of the power supply output circuit. 250.162 covers if a DC system needed to be a grounded system, and you system is not required to be a grounded system.
            Don, Illinois
            (All code citations are 2017 unless otherwise noted)