I have incoming electric utility supply into commercial church service disconnects Panelboard which is MLO with six circuit breakers. All five circuit breakers are filled go to non solar panel load and sixth circuit breaker feeds one inverter which then feeds solar panels. The sixth breaker is opposite end of the incoming panelboard service.
Since the connection is right at the service disconnect sixth breaker the question can you use NEC 2014 Article 705.12(B)(2)(3) to check panelboard bus and breaker sizes? If yes then which one NEC 2014 of 795.12(B)(2)(3)(a),b,c,d, or e. If not then which Article should be used to check breaker, panelboard size in above situation?
Thank you for your input.
Since the connection is right at the service disconnect sixth breaker the question can you use NEC 2014 Article 705.12(B)(2)(3) to check panelboard bus and breaker sizes? If yes then which one NEC 2014 of 795.12(B)(2)(3)(a),b,c,d, or e. If not then which Article should be used to check breaker, panelboard size in above situation?