Backfed PV Breaker and the Rule of Six

Status
Not open for further replies.
Hi,

I searched this forum for an answer to the question, "does a backfed PV breaker count as one of the six throws to disconnect a building from its electrical supply" (note: no batteries are in this installation), and I found an answer that was written in 2016 saying "it varies greatly by AHJ".

In 2020, is it still hotly debated, or is it clarified a bit more these days? If it does not count, what kind of evidence could I show the building department? I'm in California, which will start enforcing the NEC 2017 pretty soon.

Also, would a multimode inverter w/ a battery change the argument?

Thanks in advance.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Hi,

I searched this forum for an answer to the question, "does a backfed PV breaker count as one of the six throws to disconnect a building from its electrical supply" (note: no batteries are in this installation), and I found an answer that was written in 2016 saying "it varies greatly by AHJ".

In 2020, is it still hotly debated, or is it clarified a bit more these days? If it does not count, what kind of evidence could I show the building department? I'm in California, which will start enforcing the NEC 2017 pretty soon.

Also, would a multimode inverter w/ a battery change the argument?

Thanks in advance.

Mike Holt comes down on the side of PV not counting as a 7th handle. My local AHJ took some convincing, but in part because of some materials I brought in from one of Mike's presentations, they eventually agreed. They did, however, require that I install a bladed disco on the wall and tap the bus rather than add a seventh breaker.

To your question, though, I believe it is still very much up to the AHJ. I don't see why the presence of batteries should make a difference.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
In my experience most panelboards that provide for multiple service disconnecting breakers don't allow for seven anyway, per the label. So with panelboards I think it's usually a moot question. With disconnects and field installed conductors I don't know.

I think a multi-mode/battery inverter would change the equation if there are loads connected through it.
 