Hi All,
I have been at this awhile so have downsized a main breaker or two in my day.
The current job I am installing consists of 25 AC modules each rated at 1.33 amps a piece. 25x1.33= 33.25amps 33.25x1.25= 41.56amps
It is hard to downsize a main breaker over 1.56 amps..........is there anything I am missing that might allow this on a 40amp breaker, and therefore not require a downsize of the main?
Main panel is a QO with 200 amp main breaker.
Thanks
tortuga
Code Historian
Oregon
Electrical Design
FYI square D does make a QOM2175VH 175-Amp (I see people downsize to a 150).
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
I did the same thing a year ago with 175 amp breaker but I believe it was a ge breaker. I am pretty sure all manufacturers make them but they are not usually a stock item
jaggedben
Northern California
If it was less than half of one amp over then I think you could make a case for rounding off but I think you're stuck downsizing unless you have a very accommodating AHJ.
I agree about 175A, I never downsize to 150.
JoeNorm
WA
Yes, we stock QO 175 on the vans because we do this so often. We're just usually never this "close" to not having to downsize so I was making sure.
I'll go ahead and install the 175. It's hard knowing the array will likely never produce more than 30 amps, let alone 40-50
ggunn
Austin, TX, USA
Hi All,
Thanks
The short answer is no. You can downsize the main breaker or you can upsize the MDP bus.
But we have documentation from Eaton that their Cutler-Hammer panels from 150A to 225A all have the same 225A bus. Maybe you could query SQD and ask them if they do something similar?
Carultch
Massachusetts
The long answer, is to get your inverters derated by the factory/firmware to have slightly less output current than their standard rating, with a letter for your AHJ to accept. Probably not something that will happen for microinverters/AC modules, and not something practical for a system at this scale.
ggunn
Austin, TX, USA
He is using microinverters.