    690.64 (B)(2); Can I have a 200 amp panel fed with a 150 amp conductors, 150 amp OCD, from the Power Company, and have my Photovoltaic system feed the buss with a 60 amp OCD?

    I don't think so!
    Thanks.
    Any one seen my reading glasses?;)

    #2
    I'm not sure that I understand the question, but I think you may be reading that wrong.

    "....Supplying power to the busbar..."

    The exception says that you can go up to 120%.

    After looking into it some more you are correct:

    100 amp main = 20 amp PV
    200 amp main = 40 amp PV

    so I'm thinking that 150 amp main = 30 amp PV

    That's without doing the math of course.
    I can build anything you want if you draw a picture of it on the back of a big enough check.

    [COLOR=red]There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.[/COLOR]

    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector

    Comment


      #3
      Originally posted by cowboyjwc
      I'm not sure that I understand the question, but I think you may be reading that wrong.

      "....Supplying power to the busbar..."

      The exception says that you can go up to 120%.

      After looking into it some more you are correct:

      100 amp main = 20 amp PV
      200 amp main = 40 amp PV

      so I'm thinking that 150 amp main = 30 amp PV

      That's without doing the math of course.
      The output of a photovoltaic power source shall be connected as specified in 690.64 (A) or 690.64(B). Since this job is being connected to the Load side and it is a dwelling, SO, we have a 200 amp panel feed with 150 amp conductors and OCD,(from the Utilities) we now also fed the panel with a 60 amp OCD from the PV system, We have 210 amps of feed to the panel, we can load it to 240 amps if it is a dwelling. AS per the excep. I think. So we are in compliance. BUT, if it is not a dwelling then we have slipped into a violation as per 690.64 (B)???? HELP
      Any one seen my reading glasses?;)

      Comment


        #4
        Sorry, for some reason I just assumed that it was a residential with that size panel.

        Yes you are correct that if it were a commercial building you would be noncompliant.

        For commercial it is Main breaker + PV breaker = rating of load center. So basically for Non-Dwelling: Increase load center and use smaller main breaker.