    Originally posted by ggunn View Post
    It's not an amendment to the NEC, it's an addendum, and many AHJ's do exactly that.
    Our ordinance calls both our additions and deletions to the NEC amendments.
    Sec 22-161. Adoption of the national electrical code, 2008 with amendments.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

    Comment


      #17
      Originally posted by don_resqcapt19 View Post
      Our ordinance calls both our additions and deletions to the NEC amendments.
      Your ordinance calls out sections of the NEC to ignore? I guess that could happen though I've never seen it.

      Comment


        #18
        Originally posted by ggunn View Post
        Your ordinance calls out sections of the NEC to ignore? I guess that could happen though I've never seen it.
        Yes, there are some deletions. I think there were at least two states that deleted the AFCI rules when they first came out.
        Don, Illinois
        (All code citations are 2017 unless otherwise noted)

        Comment


          #19
          supply side connections

          What is the formulae, NEC rule, that limits the solar inverter(s) output that can be connected to a supply side tap?
          It is not the 120% of the buss bar rule, correct?

          Comment


            #20
            Originally posted by don_resqcapt19 View Post
            Yes, there are some deletions. I think there were at least two states that deleted the AFCI rules when they first came out.
            NJ was one of those states. 210.12 is now adopted but the 2005 exceptions in 210.8 (A) 2 and 5 for GFCI's are adopted into the 2011 code. You not only have to know your code you have to know the changes.
            Rick Napier
            Inspector and Instructor

            Comment


              #21
              Originally posted by beechigby View Post
              What is the formulae, NEC rule, that limits the solar inverter(s) output that can be connected to a supply side tap?
              It is not the 120% of the buss bar rule, correct?
              705.12(A), in part, says "The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service."
              I will have achieved my life's goal if I die with a smile on my face.

              Comment


                #22
                Originally posted by beechigby View Post
                What is the formulae, NEC rule, that limits the solar inverter(s) output that can be connected to a supply side tap?
                It is not the 120% of the buss bar rule, correct?
                The 120% rule applies to both busbars and conductors.

                Comment


                  #23
                  Originally posted by ggunn View Post
                  The 120% rule applies to both busbars and conductors.
                  705.12(D)(2), the 120% rule, applies only on the load side of the service disconnecting means. See 705.12(D) general requirement.
                  I will have achieved my life's goal if I die with a smile on my face.

                  Comment


                    #24
                    Meter Socket Adapters????m

                    While installing solar in central California we have come across many center fed main all in one panels. Some jurisdictions are stating that we can't use the 120% rule on these panels because it is not opposite end of the bus on the load side. Most of these panels it seems we can't fit a bug or tap into the supply side wiring.

                    I have heard of some people using socket meter adapters that extend where the meter is in the panel with a knockout and place to install supply side wiring. Does anyone know about these? Does anyone know where to get them? I can see that Solar City has a patent on one from 2010 but can not find a retailer of such a thing. Would really help out, but I am starting to feel that I am chasing a unicorn.

                    The Milbank tap connectors are a good solution but won't fit all panels, while if this socket adapter exists it should fit all panels.