fmtjfw

Senior Member
Section/Paragraph: 210.8(B) exceptions

Revised Text

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
....
(B) Other Than Dwelling Units.
....
(3) Rooftops

Exception: Receptacles on rooftops shall not be required to be readily accessible other than from the rooftop.

(4) Outdoors

Exception No. 1 to (3): Receptacles on rooftops shall not be required to be readily accessible other than from the rooftop.

Exception No. 2 to (3) and (4): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment shall be permitted to be installed in accordance with 426.28 or 427.22, as applicable.

Exception No. 3 to (4): In industrial establishments only, where the conditions of maintenance and supervision ensure that only qualified personnel are involved, an assured equipment grounding conductor program as specified in 590.6(B)(2) shall be permitted for only those receptacle outlets used to supply equipment that would create a greater hazard if power is interrupted or having a design that is not compatible with GFCI protection.

Exception to (3) and (4): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment shall be permitted to be installed in accordance with 426.28 or 427.22, as applicable.

Substantiation

The exception that applies only to (3) should immediately follow (3). The exception that only applies to (4) should immediately follow (4). The exception that applies to (3) and (4) should follow (3) and (4) as closely as is practical.

Inserted Deleted
 