230.24(A) Exception No. 2

Status
Not open for further replies.

fmtjfw

Senior Member
Section/Paragraph: 230.24(A) Exception No. 2

Revised Text

230.24 Clearances.
....
(A) Above Roofs.
....
Exception No. 2:
Where the voltage between conductors does not exceed 300, and the roof has a slope of 100 mm in 300 mm (4 in. in 12 in.) 1 in 3 or greater steeper, a reduction in clearance to 900 mm (3 ft) shall be permitted.


Substantiation

Slope is dimensionless, it is just a ratio.

Inserted Deleted
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Section/Paragraph: 230.24(A) Exception No. 2

Revised Text

230.24 Clearances.
....
(A) Above Roofs.
....
Exception No. 2:
Where the voltage between conductors does not exceed 300, and the roof has a slope of 100 mm in 300 mm (4 in. in 12 in.) 1 in 3 or greater steeper, a reduction in clearance to 900 mm (3 ft) shall be permitted.


Substantiation

Slope is dimensionless, it is just a ratio.

Inserted Deleted
There are a lot more code users who will understand 4" in 12" than will understand a 1 in 3 slope. I know it is the same, but you only hear roof slopes being talked about in the terms of "x in 12".
 