fmtjfw
Senior Member
- Location
- Fairmont, WV, USA
Section/Paragraph: 230.53
Revised Text
230.53 Raceways to Drain.
Where exposed to the weather, raceways enclosing service-entrance conductors shall be suitable listed for use in wet locations and arranged to drain. Where embedded in masonry, raceways shall be arranged to drain.
Substantiation
Requiring raceways to be listed for wet location is reasonable. Suitable is a bit wishy-washy (pun intended).
Listed for wet location is used in 300.50(B), 310.10(C)(3), 314.15, 330.10(A)(11)c., 366.6(A)(2), 366.120(2), 396.10(B)(2), Table 400.4 Note 9, 410.96, 547.5(C)(2), 547.8(C), 550.15(H), 725.179(E), and 760.179.
Inserted Deleted
Revised Text
230.53 Raceways to Drain.
Where exposed to the weather, raceways enclosing service-entrance conductors shall be suitable listed for use in wet locations and arranged to drain. Where embedded in masonry, raceways shall be arranged to drain.
Substantiation
Requiring raceways to be listed for wet location is reasonable. Suitable is a bit wishy-washy (pun intended).
Listed for wet location is used in 300.50(B), 310.10(C)(3), 314.15, 330.10(A)(11)c., 366.6(A)(2), 366.120(2), 396.10(B)(2), Table 400.4 Note 9, 410.96, 547.5(C)(2), 547.8(C), 550.15(H), 725.179(E), and 760.179.
Inserted Deleted