Section/Paragraph: 547.8(C)

Revised Text

547.8 Luminaires.
....
(C) Exposed to Water.
Luminaires exposed to water from condensation, building cleansing water, or solution shall be listed as suitable for use in wet locations.

Substantiation

"Listed as suitable" is the same as "listed", "as suitable" adds no strengthening or lessening of the requirement.

Inserted Deleted
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Section/Paragraph: 547.8(C)

Revised Text

547.8 Luminaires.
....
(C) Exposed to Water.
Luminaires exposed to water from condensation, building cleansing water, or solution shall be listed as suitable for use in wet locations.

Substantiation

"Listed as suitable" is the same as "listed", "as suitable" adds no strengthening or lessening of the requirement.

Inserted Deleted
The current code wording matches up with the marking that UL requires on the luminaire.(HYXT)
Luminaires marked "DRY LOCATIONS ONLY" are intended to be installed in indoor dry locations.​
Luminaires marked "SUITABLE FOR DAMP LOCATIONS" are intended to be installed in damp or dry locations.​
Luminaires marked "SUITABLE FOR WET LOCATIONS" are intended to be installed in wet, damp or dry locations.​

 