I have an idea for a proposal for a change to the next NEC cycle, and I was wondering what you all think about it: I wish the NEC would require all lighting circuits to be used for lights and smoke alarms only (allowing either #14 or #12 wire), then also require separate circuits to power the receptacle outlets with #12 wire only, for 20A capacity. In fact, this is already they way it is in the state of Alabama, but I think it should be part of the NEC, which would apply anywhere. This is also how I always wire new houses, regardless, even in Tennessee where I live. I use #14 for lighting, and #12 for wall receptacles.
Announcement
Collapse
No announcement yet.
Separate Lighting and Receptacle Circuits
Collapse
This topic is closed.
X
X
-
Never going to happen. Although the code isn't supposed to be a design manual it does often step over the line into this area, however, you would have to substantiate how using 14 awg on general receptacles is a safety issue. Quite frankly, it is not a safety issue.They say I shot a man named Gray and took his wife to Italy
She inherited a million bucks and when she died it came to me
I can't help it if I'm lucky
-
Originally posted by Dennis Alwon View PostNever going to happen. Although the code isn't supposed to be a design manual it does often step over the line into this area, however, you would have to substantiate how using 14 awg on general receptacles is a safety issue. Quite frankly, it is not a safety issue.
Comment
-
Originally posted by jeff48356 View PostWell, using #14 on wall receptacles limits the capacity of the circuit to 15 amps, rather than 20, so it is more likely that breakers will trip if high-current loads are plugged into them (electric heaters, vacuum cleaners, window air conditioners, etc). And, of course, overloads are always a safety issue, and the Code has taken other measures to reduce tripped breakers in recent past. For example, they now require the bathroom to be on a separate 20A circuit. And now they are requiring the same for the garage receptacles.
NEC has already recognized that we tend to have heavier loads in the kitchen laundry and bath areas and has mandated 20 amp receptacle circuits there - even that is still pushing its own rule IMO in 90.1 of not being a design specification or instruction manual though. I think it is a good idea, especially in those areas to run 20 amp circuits, and I also myself run 20 amp ciruits to nearly all 120 volt receptacle outlets as a general rule - but that is by my decision.I live for today, I'm just a day behind.
Comment
-
I almost always run#12 to everything, however I would hate having to separate lighting and receptacle loads.
Originally posted by jeff48356 View PostWell, using #14 on wall receptacles limits the capacity of the circuit to 15 amps, rather than 20, so it is more likely that breakers will trip if high-current loads are plugged into them (electric heaters, vacuum cleaners, window air conditioners, etc).
You could make each room a separate circuit to solve this issue. Bedrooms are generally lightly loaded.
Comment
-
Originally posted by kwired View PostPlug two 1500 watt heaters into a 20 amp circuit and you still overload it- where do you draw the line besides running an individual circuit to every receptacle outlet?
NEC has already recognized that we tend to have heavier loads in the kitchen laundry and bath areas and has mandated 20 amp receptacle circuits there - even that is still pushing its own rule IMO in 90.1 of not being a design specification or instruction manual though. I think it is a good idea, especially in those areas to run 20 amp circuits, and I also myself run 20 amp ciruits to nearly all 120 volt receptacle outlets as a general rule - but that is by my decision.Electricians do it until it Hertz!
Comment
-
Originally posted by JFletcher View PostIf you have both 600 and 900W switches on on both heaters. Older homes with half the house on one 15A circuit, you'd be lucky to run one 1500W heater @ 900W and keep the lights on.I live for today, I'm just a day behind.
Comment
-
Originally posted by Coppersmith View PostI almost always run#12 to everything, however I would hate having to separate lighting and receptacle loads.
Comment
-
Originally posted by jwelectric View PostWould this mean they would delete 210.70(A)(1) exception
Who are you?Disappear for years, you don't show up at the big meet in Raleigh.... Hope you are doing well.
They say I shot a man named Gray and took his wife to Italy
She inherited a million bucks and when she died it came to me
I can't help it if I'm lucky
Comment
-
-
Originally posted by Dennis Alwon View PostWho are you?Disappear for years, you don't show up at the big meet in Raleigh.... Hope you are doing well.
Mike Whitt
[COLOR=#000066]God answers Knee-Mail. [/COLOR]
Comment
-
Originally posted by jeff48356 View PostFor the big meet in Raleigh.. are you referring to IBMA? If so, I am attending that!!
No, I was talking about one of the largest conventions on electrical codes in the country. 700 of us whackos show up in April and talk about the electrical trade, codes, etc. It's put on by the NC board of electrical examiners. It is called NC institute
Jwelectric, as well as a few other Mike Holt members, have shown up. Even Mike Holt was there last AprilThey say I shot a man named Gray and took his wife to Italy
She inherited a million bucks and when she died it came to me
I can't help it if I'm lucky