210.52(B)(1) Exception No. 1
[Delete text]
(1) 210.52(B)(1) Exception No. 1 is unnecessary. It doesn't effect the application of either 210.52 or 210.70.
(2) The exception and the context of it's use can be difficult to interpret correctly. The phrase "permitted in lieu of lighting outlets" in 210.70(A)(1) Exception No. 1 causes the switched receptacle to be seen as a receptacle outlet allowed by 210.52.
(3) It is clearer to disallow the receptacle's connection to the small appliance circuits under 210.52(B)(2).
_______________________________________________________________________________
Again, I don't have 2005.
I want to be sure that this can't be construed as prohibiting switching a 210.52 receptacle for another purpose.
Any thoughts on whether I've pulled it off?
I'm still a little concerned that if there are two outlets that meet the definitions of 210.70, they might both be seen as "required" by 210.70 and cause a problem with inspectors thinking you can't switch an SA receptacle.
[Delete text]
[Add text]210.52(B)(1) Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permitted.
[Substantiation]210.52(B)(2)(a) A wall switch controlled receptacle used in lieu of a lighting outlet required by 210.70(A) shall not be supplied by the two or more small-appliance branch circuits specified in 210.52(B)(1).
(1) 210.52(B)(1) Exception No. 1 is unnecessary. It doesn't effect the application of either 210.52 or 210.70.
(2) The exception and the context of it's use can be difficult to interpret correctly. The phrase "permitted in lieu of lighting outlets" in 210.70(A)(1) Exception No. 1 causes the switched receptacle to be seen as a receptacle outlet allowed by 210.52.
(3) It is clearer to disallow the receptacle's connection to the small appliance circuits under 210.52(B)(2).
_______________________________________________________________________________
Again, I don't have 2005.
I want to be sure that this can't be construed as prohibiting switching a 210.52 receptacle for another purpose.
Any thoughts on whether I've pulled it off?
I'm still a little concerned that if there are two outlets that meet the definitions of 210.70, they might both be seen as "required" by 210.70 and cause a problem with inspectors thinking you can't switch an SA receptacle.