Put 334.15(C) back the way you found it.

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
1.) NEC Section/Paragraph: 334.15(C)
2.) Proposal Recommends: [deleted text]
3.) Proposal: NEC-2005 334.15(C) has the following added after the existing 2002 text:

NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing. Conduit or tubing shall utilize a nonmetallic bushing or adapter at the point this cable enters the raceway. Metal conduit and tubings and metal outlet boxes shall be grounded.


4.) Substantiation: The statement "NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing." is redundant, as it is already stated in 300.18, and 300.15(C).

The statement "Conduit or tubing shall utilize a nonmetallic bushing or adapter at the point this cable enters the raceway." is overly restrictive, as a bushing is already required by 300.15(C). A properly installed metallic connector can be used anywhere except in an unfinished basement? That isn't logical or reasonable.

The statement "Metal conduit and tubings and metal outlet boxes shall be grounded." is in direct contradiction to 250.86 exception 2, which rightly assumes that cables being protected from outward physical damage are going to be intact on the interior of that protection.

______________________________________________

How the heck was this passed in the first place? Does anybody have the ROP and ROC on this???

[ April 24, 2005, 01:18 PM: Message edited by: georgestolz ]
 

jwelectric

Senior Member
Location
North Carolina
Re: Put 334.15(C) back the way you found it.

George
There was a few changes made to 334.15 from ?02 to ?05. Note in (B) some of the wording has been removed such as, pipe, guard strips, listed surface metal or nonmetallic raceway, or other means. Also notice that the word approved was added to or other means.

The words, NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing. Conduit or tubing shall utilize a nonmetallic bushing or adapter at the point the cable enters the raceway. Metal conduit and tubing and metal outlet boxes shall be grounded, was added to (C).
The mention of bonding the metal conduit and box was to clear any misunderstanding that might construed from 250.86 Exception No. 2: which states, Short sections of metal enclosures or raceways used to provide support or protection of cable assemblies from physical damage shall not be required to be grounded.

I hope this helps to clear things up just a little. If you still need the ROPs I will be glad to PM them to you.
:)
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Put 334.15(C) back the way you found it.

I'd love to see it. You can put it on this thread, that's all right. :)

The mention of bonding the metal conduit and box was to clear any misunderstanding that might construed from 250.86 Exception No. 2...
What's to be misunderstood? Now I have to put a metal box in my basement, run my flex from the ceiling all the way into the box, in order to bond the flex that was never going to have a chance to be energized anyway. Actually now I can't use FMC, I have to use LFNC, which is inferior to the FMC I was using in the first place.

Everywhere else in the code assumes that the protection is going to protect the cable, and that the cable isn't going to energize anything else unless it is damaged. Yet, suddenly, in unfinished basements only, the FMC has to be bonded, and a nonmetallic bushing must be used.

Of course, there was that guy that was stabbed to death with that dangerously sharp flex connector... :roll:
 

jwelectric

Senior Member
Location
North Carolina
Re: Put 334.15(C) back the way you found it.

7-131 Log #1827 NEC-P07
(334-15(A) Exception (New) )
Final Action: Reject
Submitter: David Zinck, NewburyPort Wiring Inspector
Recommendation:
Add an exception to read as follows:
Exception: Stacker devices designed for the purpose shall be allowed to secure the cable where installed in accordance with (a) and (b)
below:
(a) the stacker devices are installed at intervals no greater than 600 mm (2 ft) and,
(b) the wire enters the stacker device from the top or the side.
Substantiation:
Stacker devices provide a very handy, safe, and neat way to do home runs in a house. With the cable supported at a maximum of 2 ft the spport is equivalent to runing through holes in studs. The purpose of (b) is to ensure that the wire snaps down into the device. If the devices were installed with the openings to the bottom, not much cable would have to fall out before the weight of the cable would pull the wire out of the others. Also, there is at least one manufacturer that has a device that the wires snap into on both sides. On such a device only the top half could be used on horizontal runs.
Panel Meeting Action: Reject
Panel Statement:
334.30 does not prohibit using this type of device.
Number Eligible to Vote: 15
Affirmative: 14 Negative: 1 Ballot Results:
Explanation of Negative:
BROWN: The panel statement concerning 334.30 indicated that the use of "stacker devices" are not prohibited by the NEC. This proposal would recognize and regulate their use in an installation and should be considered.


7-132 Log #1239 NEC-P07
(334-15(B))
Final Action: Accept
Submitter: David H. Kendall, Carlon, Lamson & Sessions
Recommendation:
Revise text to read as follows:
(B) Protection from Physical Damage. The cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, pipe, guard strips, listed surface metal or nonmetallic raceway, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, listed surface metal or
nonmetallic raceway, or other metal pipe or other approved means extending at least 150 mm (6 in.) above the floor.
Substantiation:
Pipe, guard strips, listed surface metal or nonmetallic raceways are not listed for areas of physical damage and should not be referenced. These raceways and methods will not provide the physical strength required to protect the NM cable in an area that has been determined as an area of physical damage.
Panel Meeting Action: Accept
Number Eligible to Vote: 15
Affirmative: 15 Ballot Results:


7-133 Log #1805 NEC-P07
(334-15(B))
Final Action: Reject
Submitter: William A. Wolfe, Steel Tube Institute of North America
Recommendation:
Revise to read:
Where subject to physical damage tThe cable shall be protected from physical damage where necessary by...
Substantiation:
This text is consistent with that used throughout the NEC for wiring methods that may be subject to physical damage. It makes it clear
that physical protection is always to be provided where the cable is subject to physical damage.
Panel Meeting Action: Reject
Panel Statement:
The action on Proposal 7-132 explains how the cable must be protected where subject to physical damage.
Number Eligible to Vote: 15
Affirmative: 15 Ballot Results:
831


Report on Proposals ? May 2004 NFPA 70
7-134 Log #2037 NEC-P07
(334-15(B))
Final Action: Accept
Submitter: National Electrical Code Technical Correlating Committee
Recommendation:
This suggested change would move the text from 334.10(B)(3) to a new sentence at the end of 334.15(B) as
follows:
(B) Protection from Physical Damage. The cable shall be protected from physical damage where necessary by conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, pipe, guard strips, listed surface metal or nonmetallic raceway, or other means. Where passing through a floor, the cable shall be
enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, listed surface metal or nonmetallic raceway, or other metal pipe extending at least 150 mm (6 in.) above the floor.
Where Type NMC cable is installed in shallow chases in masonry, concrete, or adobe, the cable shall be protected against nails or screws by a steel plate at least 1.59 mm (1/16 in.) thick and covered with plaster, adobe, or similar finish.
Substantiation:
This information was previously located under "uses permitted" and should more appropriately be inserted within Section 334.15(B) since this section is dealing with protection from physical damage. During the processing of the 2002 NEC, a code-making panel identified concerns with the concept of trying to describe the "uses permitted" for a particular wiring method and not be in conflict with the "uses not permitted". In some cases, the permitted and "not permitted" uses can be easily segregated. However, there are a number of instances where the "use permitted" ends up being the exception to a "use not permitted".
Because of the problems becoming apparent with the lists, the Correlating Committee asked the Usability Task Group to review the issue and make a recommendation on how to best handle the lists.
With these revisions, the NEC language would only cover those specific "uses not permitted" for a wiring method. All applications not covered by those limitations would be acceptable.
This is a companion proposal to revise 334.12 to include the Uses Permitted Language.
This would make it easier for inspectors, manufacturers, electricians, and others in the electrical industry to determine what uses were not permitted for this wiring method without making it necessary for the Code Panels to provide a running laundry list of uses permitted. The Useability Task Group on Uses Permitted/Uses Not Permitted is comprised of Mr. George Dauberger,
Mr. John Minick, Mr. Jim Dollard, Mr. Dick Owen, Mr. Phil Sutherland, and Mr. Mark Ode.
Panel Meeting Action: Accept
Number Eligible to Vote: 15
Affirmative: 15 Ballot Results:


7-135 Log #1240 NEC-P07
(334-15(C))
Final Action: Reject
Submitter: David H. Kendall, Carlon, Lamson & Sessions
Recommendation:
Revise text to read as follows:
(C) In Unfinished Basements. Where the cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards. NM cable used on a wall of a unfinished basement shall be installed in a listed conduit or tubing. Conduit or tubings shall utilize a nonmetallic bushing or adapter at the point where the cable enters the raceway. Metal conduit and tubings and metal outlet boxes shall be grounded.
Substantiation:
This proposal is to clarify that NM cable used in an unfinished basement must be installed into a raceway when coming down a wall to a device box. The nonmetallic bushing or adapter for the raceways is required to prevent possible damage to the sheathing on the cable. All metal components are required to be grounded.
Panel Meeting Action: Reject
Panel Statement:
334.15(A) and (B) address the submitter's concerns.
Number Eligible to Vote: 15
Affirmative: 15 Ballot Results:
832

This is a little lengthy but you ask for it. As you can see there was a little action before it made it to the comment stage but it is clear to see what was being attempted here.

If you use a metal raceway to protect NM cable on a basement wall then a metal box will be required and they must be bonded. See, 314.3 Nonmetallic Boxes, Exception 1 and 2.

The nonmetallic fitting was introduced because the pipe should be as high as the joist and this causes damage to the NM cable if no fitting is installed.

Again I hope this helps.

[ April 25, 2005, 02:30 PM: Message edited by: jwelectric ]
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Put 334.15(C) back the way you found it.

Thanks, JW. :)

Substantiation:
This proposal is to clarify that NM cable used in an unfinished basement must be installed into a raceway when coming down a wall to a device box. The nonmetallic bushing or adapter for the raceways is required to prevent possible damage to the sheathing on the cable. All metal components are required to be grounded.
Panel Meeting Action: Reject
Panel Statement:
334.15(A) and (B) address the submitter's concerns.
So when did the wheels fall off? Did the CMP have a change of heart at the ROC stage?

That's just it--it doesn't belong solely to (C) if it's a general problem. It belongs in (A)&(B), like the CMP originally stated.

It's still contradictory to the citations I noted in my substantiation. How did they overlook that? :confused:
 

jwelectric

Senior Member
Location
North Carolina
Re: Put 334.15(C) back the way you found it.

George
This is a time consuming way to find them but here is the link use the codes and standards tab and then ROP ROC ect.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Put 334.15(C) back the way you found it.

Ok, thanks JW.

I just looked at it, and am confused. In the ROP you posted, it said "Reject." In the ROC, it said the Meeting action was "Accept." Maybe I'm not reading it correctly.

What's the difference between "Accept" and "Accept in Principle"?
 

jwelectric

Senior Member
Location
North Carolina
Re: Put 334.15(C) back the way you found it.

Charlie Eldridge could do a better job with an answer on this but I will give it a try.

The CMP can make one of four calls on a proposal. They are: accept, accept in part, accept in principal or reject.

If I was a panel member I would every thing accepted in principal so I could play with it.

There was a lot of action going on in 334.15 so when it got to the comment stage they played with it a little, made it so it could be debated either way, and wrote the new article.
:)
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Put 334.15(C) back the way you found it.

So "accept" is totally accepted, and the others they can modify to their own liking? Makes sense.