    Here is another one to drive you crazy. This entire section is new
    210.52(C)(2) Island and Peninsular Countertops and Work Surfaces.
    Receptacle outlets shall be installed in accordance with 210.52(C)(2)(a) and (C)(2)(b). (a)At least one receptacle outlet shall be provided for the first 0.84 m2 (9 ft2), or fraction thereof, of the countertop or work surface. A receptacle outlet shall be provided for every additional 1.7 m2 (18 ft2), or fraction thereof, of the countertop or work surface.
    (b)At least one receptacle outlet shall be located within 600 mm (2 ft) of the outer end of a peninsular countertop or work surface. Additional required receptacle outlets shall be permitted to be located as determined by the installer, designer, or building owner. The location of the receptacle outlets shall be in accordance with 210.52(C)(3).
    A peninsular countertop shall be measured from the connected perpendicular wall.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
    #2
    Why are they basing the receptacle spacing on square footage?. We just got the linear stuff straightened out not that long ago so we didn't have to use the depth dimension in the spacing. It would have been easier to use the logic of receptacles for showroom windows since most counters are 2 foot deep.
    Stuff like this makes it in, but a valid proposal doesn't because it wasn't formatted correctly according to the style guide. Shaking head. If feel like Gibbs needs to head slap someone.
    Comment
      #3
      Going to see if I got this...
      From 2017 we measure from the back of the wall.
      so now if the peninsula is shorter than 3’, we get an outlet.
      If its over 3’, we get another one up to a ~9’ peninsula.
      PLUS the one at the end.
      Yes?
      Comment
        #4
        Yes?
        That is 9 sq. ft not 9 linear feet
        Comment
          #5
          Yeah, but the counter being somewhere around 34” divides out to about 9’ with the first part added
          the first 9’sq is about 3’ long, unless it’s a weird counter setup. Then the 18 sq ft added makes somewhere around 9’.
          like was stated above, it was easier to just measure lineal ft
          now if you have a “standard” countertop, it’s one measurement, if you have a bigger countertop or a stepped countertop, it’s another measurenment.
          the homeowner has a peninsula built, you figure and add receptacles. The GC or the cabinet guy talks them into a bigger slab.
          crap, just failed inspection...
          homeowner is now mad because you just added to your quote.