ryan_618 said:
Does a metal raceway that penetrates a rooftop vertically and enters directly into the bottom of a disconnect (cutout box) have to comply with the ampacity adjustment rules of (new) section 310.15(B)(2)(c)? If yes, is there any way around derating the conductors?
After a quick peak at the change, here is my take.
Yes, the raceway penetrating the roof and installed in a vertical position will require derating - "installed in conduits exposed to direct sunlight ON or ABOVE rooftops."
Notice this says
CONDUITS and
EXPOSED TO DIRECT SUNLIGHT
I would think they were very specific in this wording.
If so, then raceways may not be the proper term, but conduits which include...RMC, IMC and RNC. I wonder, by the wording they chose, if they meant to not include EMT-electrical metallic
TUBING ?
What about a trough (wireway) installed in rooftop locations?