Annex G Reference is to the original proposed article now described as Article 708.

"(D) Maintenance and Testing.​
SCADA systems shall be maintained and tested in accordance with 585.60(D)(1) and (D)(2)." :confused:

 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Joe,
The whole issue is confusing to me when you look at the ROP, Draft and the ROC. It looks like the text in question should have been made a part of the Annex per comment 20-17a. At this point the only place the referenced text shows up is on page 616 of the ROP.
Don
 