2-165 Log #529 NEC-P02 Final Action: Reject
(210.12(B))
_______________________________________________________________
Submitter: George H. Little, Little Enterprises
Recommendation: Revise text as follows:
Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch
circuits supplying outlets installed or extended in dwelling unit family rooms,
dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms,
recreation rooms or areas shall be protected by a listed arc-fault circuit
interrupter, combination-type, installed to provide protection of the branch
circuit.
Substantiation: The current wording implies that it is only that the new branch
circuits are required to have arc-fault protection. Inserting the words ?or
extended? will provide for protection of not only the new branch circuits but
also any new wiring installed as an extension of an otherwise non-AFCI
protected circuit.
Panel Meeting Action: Reject
Panel Statement: The decision on applying the new construction AFCI
requirements to a circuit modification is that of the authority having
jurisdiction.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 9 Negative: 2 Abstain: 1
...