Shunt Trip Breaker for Safety Shutdown

Status
Not open for further replies.
I was wondering if it is OK to use a shunt trip, 480VAC, breaker with a 24VDC control circuit as a safety shutdown in a SIL 3 safety circuit? Is one breaker sufficient, or will it be necessary to have two shunt trip breakers in series?
 

Timbert

Member
Location
Makawao, Hawaii
It is essentially impossible to meet the requirements of SIL 3 with a single disconnecting means. To do so the device in question must have a Safe Failure Fraction of >99% (i.e. in this case, 99% of the failures of a shunt trip breaker would have to open)[IEC 62061 6.7.6.3].

I don't know of any SIL rated shunt trip breakers. The main reason is probably that shunt trip breakers unlike relays and contactors don't default to a safe state in the event of a loss of power to the control circuit. Think of it this way, if the wire to the shunt trip coil falls off you're screwed, you can't stop the machine; if the wire to a contactor coil falls off, you lose power and the machine comes to a stop, inconvenient but safe.
 
Thanks for your response. If a UPS supplied control circuit was used for the tripping function, would a single breaker be enough? I realize it is still not fail safe, but it is a better solution.
 

Timbert

Member
Location
Makawao, Hawaii
Thanks for your response. If a UPS supplied control circuit was used for the tripping function, would a single breaker be enough? I realize it is still not fail safe, but it is a better solution.

Yes, it is a better solution, it is not a SIL 3 solution.

I will repeat what I said in my first reply: "It is essentially impossible to meet the requirements of SIL 3 with a single disconnecting means."

SIL 3 requirements are very demanding. A SIL 3 system should have a dangerous failure rate less than once per 10 million hours of operation (roughly 1140 years).

A SIL 3 solution also requires a detailed analysis of the hazards and behavior of the controls in the presence of a fault. It is not as simple as buying a SIL 3 rated component or building in redundancy.
 