    Remote Switch Actuators

    Are remote switch actuators reliable and does NFPA 70e address their use? An example in the link below.
    Any comments from persons with experience of remote switch actuators would be appreciated.

    https://cbsarcsafe.com/products/remo...itch-operators
    Last edited by TVH; 05-07-18, 10:09 AM. Reason: spelling and grammer

    #2
    Seems it reduces the need or level of PPE needed when operating some switches.

    Wouldn't change a thing when it comes to PPE needed when verifying whether there is any voltage.
    I live for today, I'm just a day behind.

    Comment


      #3
      Originally posted by TVH View Post
      Are remote switch actuators reliable and does NFPA 70e address their use? An example in the link below.
      Any comments from persons with experience of remote switch actuators would be appreciated.

      https://cbsarcsafe.com/products/remo...itch-operators
      Not sure what the question is? 70E addresses PPE required when operation or racking breakers inside the arc flash boundary, these devices allow you to do that from outside the AFHB so nothing to specifically address in the 70E about them.

      Comment


        #4
        Zog are you saying PPE is required to operate a breaker, according to what PPE is required on the label inside the Arc Flash Boundary ?

        Comment


          #5
          Originally posted by Davebones View Post
          Zog are you saying PPE is required to operate a breaker, according to what PPE is required on the label inside the Arc Flash Boundary ?
          This was answered in your other thread, depends on conditions.