    #16
    Seems the tenured sparks aways have their anecdotals.

    Myself i was blind for what was the worst 5 minutes of my life......so far...

    None of this is necessarily our own neglect , miswiring, whatever....

    You guys all know the 'ol bold electrician addage .....

    ~RJ~

    Comment


      #17
      Originally posted by Strathead View Post
      Can you quote a source that requires PPE when all covers are in place?
      yeah. me.

      i closed a main breaker on a residential panel, with all the
      covers properly in place. the arc came crawling out between
      the cutout hole, and the edge of the breakers, burnt the skin
      off the back of the middle two fingers on my right hand..

      you need to wear PPE. you can quote me if you need to.
      ~New signature under construction.~
      ~~~~Please excuse the mess.~~~~

      Comment


        #18
        Originally posted by Fulthrotl View Post
        yeah. me.

        i closed a main breaker on a residential panel, with all the
        covers properly in place. the arc came crawling out between
        the cutout hole, and the edge of the breakers, burnt the skin
        off the back of the middle two fingers on my right hand..

        you need to wear PPE. you can quote me if you need to.
        Yet we are required by code make these things readily accessible, which is also readily accessible to the unqualified, makes a lot of sense right?

        But OSHA is only for the employed, so what if others are in any danger I guess. Now comes the manager at an office building or other employee in similar situation that doesn't ordinarily do any electrical work tasks that tries to reset a tripped breaker in their office building - I guess we should at least be putting big warning signs on this equipment that only qualified individuals can even open the dead front cover and operate any devices inside, though I anticipate even that will get ignored most the time.

        Typical dwelling, the available incident energy isn't that high all that often to be able to do that, but sometimes it is.
        I live for today, I'm just a day behind.

        Comment


          #19
          Originally posted by Strathead View Post
          If all covers are in place, there should be no requirement for PPE and no more risk than that of getting struck by lightning on a sunny day. The only caveat would be a true bolted fault on a breaker who's AIC rating was calculated so incorrectly that the hedge factors in everything are overcome.
          Originally posted by Strathead View Post
          Can you quote a source that requires PPE when all covers are in place?
          In Table 130.7(C)15(A)(a) where they provide the list of appropriate PPE for tasks, it says the following under the task of operating a circuit breaker:
          Under the column heading "Equipment Condition", no additional PPE is required only if;
          All of the following:

          The equipment is properly installed
          The equipment is properly maintained
          All equipment doors are closed and secured
          All equipment covers are in place and secured
          There is no evidence of impending failure
          But, under the following conditions, yes, PPE IS REQUIRED if:
          One or more of the following:

          The equipment is not properly installed
          The equipment is not properly maintained
          Equipment doors are open or not secured
          Equipment covers are off or not secured
          There is evidence of impending failure

          Should there be an injury and a door WAS closed, an OSHA inspector is going to demand DETAILED RECORDS of whether the equipment was properly installed and maintained. The reality is, almost NOBODY has records like that.


          And BEFORE that, they provide this "Informational Note"
          Informational Note No. 2: The collective experience of
          the NFPA 70E Technical Committee is that, in most cases,
          closed doors do not provide enough protection to eliminate
          the need for PPE in situations in which the state of the
          equipment is known to readily change (e.g., doors open or
          closed, rack in or rack out).
          __________________________________________________ ____________________________
          Many people are shocked when they discover I am not a good electrician...

          I'm in California, ergo I am still stuck on the 2014 NEC... We'll get around to the 2017 code in around 2021.

          Comment


            #20
            One guy I worked with told a friend of his died after he left a wrench against the busbars in a residential panel and turned on the breaker. This was in the context of replacing a 200A main breaker on a resi panel and the guy stood to the side and used a broom stick to turn on the replacement. Just in case.

            It's not the breaker that will blow up, most times.

            Comment


              #21
              Originally posted by Jraef View Post
              In Table 130.7(C)15(A)(a) where they provide the list of appropriate PPE for tasks, it says the following under the task of operating a circuit breaker:
              Under the column heading "Equipment Condition", no additional PPE is required only if;
              But, under the following conditions, yes, PPE IS REQUIRED if:

              Should there be an injury and a door WAS closed, an OSHA inspector is going to demand DETAILED RECORDS of whether the equipment was properly installed and maintained. The reality is, almost NOBODY has records like that.

              And BEFORE that, they provide this "Informational Note"
              Jraef, Sir, You are one 70E Code cycle off!
              70E 2018 now has Table 130.5(C) Estimate of likelihood of Occurrence of an Arc Flash incident ... and that table defines Normal with 6 conditions that adds "used in accordance with instructions... to the 2015 list.

              NFPA 70E, Standard for Electrical Safety in the Workplace is a National Consensus Standard document and as such it's in effect when issued. Unlike NFPA 70 NEC which is voted in by jurisdictions. The logic is that if a Safety improvement has been recognized it's in effect right away.
              Of course 70E is not the law, but, (and I think you may have said this in a post some time ago), if there's an electrical fatality at your facility and OSHA shows up, if you don't adhere to 70E, the whole focus of the investigation will turn to comparing your practice to the 70E standard, and good luck with that.
              And the newest wrinkle to Electrical Safety is the release of IEEE 1584-2018, referenced of course by NFPA 70E, which changes the way arc flash studies are conducted. I welcome it because it's confusing enough that it'll keep me gainfully employed for years to come!

              Comment


                #22
                I’ve always felt that statistically, as an electrician, it’s more likely to blow up on you than anyone else.


                Sent from my iPhone using Tapatalk
                Brought to you by Carl's Jr.

                Comment


                  #23
                  How do you not stand in front of a I-line 480 v , 600 amp breaker if you have to close it ? Do they make a remote operator for a I-Line style breaker ?

                  Comment


                    #24
                    They make a 'handle' that allows some leverage , but it's usually not very long ~RJ~

                    Comment


                      #25
                      Originally posted by Davebones View Post
                      How do you not stand in front of a I-line 480 v , 600 amp breaker if you have to close it ? Do they make a remote operator for a I-Line style breaker ?
                      Yes, page 108

                      https://www.cbsarcsafe.com/wp-conten...2015_lores.pdf

                      Comment


                        #26
                        Originally posted by Davebones View Post
                        How do you not stand in front of a I-line 480 v , 600 amp breaker if you have to close it ? Do they make a remote operator for a I-Line style breaker ?
                        Don't laugh and it probably isn't done all that much, but standing off to side and use something for a push stick will put you further away from potential blast than using your bare hand directly on the handle.
                        I live for today, I'm just a day behind.

                        Comment


                          #27
                          We have had instances where a wiring fault or defective component caused an arc flash upon the first power up. We have engaged the 200A disconnect on new MCC's and had breakers explode, once had a VFD that blew the MOV's out of the case due to wiring faults etc.
                          So yes the first power up is a time for utmost safety prep...