    Too much corrosion

    Is there a code article I can site that requires replacement of corroded switchboard enclosures (bottom completely rusted away)? 110.7 Wiring integrity?

    #2
    Not really, though it may affect what you do replace it with.

    NEC isn't really that much about evaluating what is existing for the purpose of determining if it is safe to continue to use, but such conditions do help set a floor for how corrosive the area may be when it comes to selecting new equipment.

    Now depending on circumstances simply drilling weep holes in what was there could possibly have impacted how long it lasts if the reason for corroding away was mostly due to condensation buildup and not because of high amounts of corrosive agents.
    I live for today, I'm just a day behind.

    Comment


      #3
      The path forward seems obvious to me, it is time to remove and replace, but, not to the owner. The entire bottom of the switchboard(s) and disconnects are missing due to corrosion. Looks like years of neglect and possible flood damage along with close proximity to salt water.

      Comment


        #4
        I think it would be a basic violation of 110.3. The equipment is no longer suitable for the intended use.
        __________________________________________________ ____________________________
        Many people are shocked when they discover I am not a good electrician...

        I'm in California, ergo I am still stuck on the 2014 NEC... We'll get around to the 2017 code in around 2021.

        Comment


          #5
          If the corroded switch board is under the control of technically qualified staff with a safety plan in place, there may not be issue, IMHO.

          Comment


            #6
            NEC is an installation code not a maintenance code.

            The fact the bottom rusted out doesn't mean any NEC code was violated, just that determining conditions of the application may not have been what designer had expected.
            I live for today, I'm just a day behind.

            Comment


              #7
              What did the customer call you to do? I’ve gotten tired of arguing with people about unsafe equipment. If I don’t need to go into the equipment, let them keep as is and take the risk.
              Yes, I'll be happy to do a first class job for less than anyone else and take a dollar a week for 10 years.

              Comment


                #8
                Originally posted by Benjy View Post
                Is there a code article I can site that requires replacement of corroded switchboard enclosures (bottom completely rusted away)? 110.7 Wiring integrity?
                Is it rusted away to the point it is basically open (like you can stick your hand in the enclosure w/out removing a cover)?

                Or is it sitting on concrete and the bottom is rusted but still there.

                How are the sides of the enclosure?

                How about the interior, what condition?

                Got pics?

                Comment


                  #9
                  The original installation should have complied with 110.3(A)(1) and 110.11. The question is if it didn't comply initially does it now need to be replaced?