    Voltage and Current Dectector Hard Hat Attachment

    See this link for info on this latest detection device: https://www.safeguardequipment.com/

    Would appreciate comments on this device with respect to reliability and limitations.

    #2
    I guess if you are working around MV or HV power lines it could be OK as a general safety aid. You have to be closer than 4ft from 2400V L-N for it to detect anything, that's already pretty close if it's a bare conductor. No mention of whether it would pick up voltage in a conduit or behind an enclosure door. If you were knowingly working that close to potentially live conductors, you would have wanted a hot stick tester on it before you got that close.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

    I'm in California, ergo I am still stuck on the 2014 NEC... We'll get around to the 2017 code in around 2021.

    Comment


      #3
      The thread title says voltage and current detection. The video only mentions voltage detection. Current detection (unbalanced only) would be possible through conduit or equipment enclosures. Voltage detection would not.

      Comment


        #4
        While it's a neat bent on non contact testers, methinks most of us would not trust our lives w/them....~RJ~

        Comment


          #5
          Originally posted by GoldDigger View Post
          The thread title says voltage and current detection. The video only mentions voltage detection. Current detection (unbalanced only) would be possible through conduit or equipment enclosures. Voltage detection would not.
          Where there is voltage 30 KV and above there is this phenomenon called corona.

          Not the six-pack variety.

          Where there is corona there is UV/IR. These belong to the light spectrum not visible to humans.
          Although short -time exposure may not be harmful—prolonged or sustained could be harmful—and they can be readily detected.

          Comment


            #6
            Originally posted by romex jockey View Post
            While it's a neat bent on non contact testers, methinks most of us would not trust our lives w/them....~RJ~
            That would be my take on the device.

            The highest voltage kit I've worked on was 11kV for which we had a tester. A stick.[LIST=1][*]Test the tester - it had a tester accessory for that.[*]Check that the circuit to be worked on is dead.[*]Retest the tester to verify that is still indicating correctly.[*]Ground (earth) the circuit to be worked on.[/LIST]

            No mention was made of how steps 1 and 3 would be carried out with the non-contact tester.