    Pallets in front of panel.

    We installed a row of machines directly in front of the wall with all our panels & disconnects, leaving about 50 inches of space behind the machines for access to the panels.
    Unfortunately the workers are just barely able to squeeze a row of bins and pallets into this space, completely blocking the entire wall, including the main panel.
    The fire inspector always cites this, so they move the pallets, take a picture for her, then move the pallets back.
    As an electrician, this burns me up (figuratively, so far) but I am not 'empowered' to do anything about it. They will tell me it is a necessary part of the work flow.

    How many of you think I am an idiot for tolerating this.

    #2
    If you are not getting any back up from management you could send a picture to OSHA and L&I
    RichB N7NEC

    Comment


      #3
      Not really your problem, other than make them move all that stuff each and every time.
      Tom
      TBLO

      Comment


        #4
        It's not something I ever worry about.
        If Billy Idol is on your playlist go reevaluate your life.

        Comment


          #5
          Originally posted by ptonsparky View Post
          Not really your problem, other than make them move all that stuff each and every time.
          And that's time on your clock. even if it's just watching.

          Comment


            #6
            Originally posted by rabtrfld View Post
            We installed a row of machines directly in front of the wall with all our panels & disconnects, leaving about 50 inches of space behind the machines for access to the panels.
            Unfortunately the workers are just barely able to squeeze a row of bins and pallets into this space, completely blocking the entire wall, including the main panel.
            The fire inspector always cites this, so they move the pallets, take a picture for her, then move the pallets back.
            As an electrician, this burns me up (figuratively, so far) but I am not 'empowered' to do anything about it. They will tell me it is a necessary part of the work flow.

            How many of you think I am an idiot for tolerating this.
            This is really the fire inspector's thing to worry about. Were I he, at the third time I came in and saw this it would be a $500 fine, or whatever maximum for the third offense is, and use whatever multipliers since it's willful. I'd also direct the plant to paint the area in front of the panels yellow or hash the area yellow and have them post a "No storage in yellow floor space" sign. And then when I came in the fourth time and saw it again I'd double the fine. Rinse and repeat until they get the message.

            Comment


              #7
              Originally posted by ptonsparky View Post
              Not really your problem, other than make them move all that stuff each and every time.
              Unless you need to get in there for a real emergency, then yes, it is kinda your problem.

              Comment


                #8
                Originally posted by Timbert View Post
                Unless you need to get in there for a real emergency, then yes, it is kinda your problem.
                I’m thinking as an outside contractor. Usually an emergency is well over by the time I’m there. I’ve never been afraid to tell owners/managers to move stuff, I’ll move it on their dime or call me when it’s clear. They know what needs to be done.
                Tom
                TBLO

                Comment


                  #9
                  I once pointed out a glaring electrical hazard to someone as I walked through a lumber mill on my way to a project. I wasn't there to address it, but I couldn't un-see it. The next time I went there nothing had changed, and I said something again as a "friendly reminder". 6 months later I went back for something else and that part of the mill had burned down; turned out the thing I pointed out was the cause. I said nothing, but the guy I had originally pointed it out to saw me and told me that he should have listened to me. Then he half jokingly accused me of sabotage in order to make my point. Thank goodness I was in another state when the fire happened...
                  __________________________________________________ ____________________________
                  Many people are shocked when they discover I am not a good electrician...

                  I'm in California, ergo I am still stuck on the 2014 NEC... We'll get around to the 2017 code in around 2021.