matthew boyd
Member
I have a question reguarding a set of Vaccumes we use at work. Here is what I know. They are not UL listed, they are rated at 18A, 2000 W, 2.6 HP. They have been tested to draw 17A in normal use with a clamp on current meter. They came with a molded on 15A plug on a 14/3 SJTOW type cable.
As near as I can tell the 14/3 cable does pass specs though just barely. However the 15A plug seems painfully inadiquate and in my opinion poses a safety risk.
The problem is compounded when the plug ends began to fail and they were being replaced with 15A screw on replacement plugs.
Would anyone know a specific regulation that relates to this. The only thing I could find relates to the maximun draw of a single device to be limited to 80 % of the branch circuit, but it doesn't necisarily say that the plug has to be correct size (although common sense would tell you it does) just that the branch circuit is sufficiant.
Thanks for any time you can give me on this.
Matt
As near as I can tell the 14/3 cable does pass specs though just barely. However the 15A plug seems painfully inadiquate and in my opinion poses a safety risk.
The problem is compounded when the plug ends began to fail and they were being replaced with 15A screw on replacement plugs.
Would anyone know a specific regulation that relates to this. The only thing I could find relates to the maximun draw of a single device to be limited to 80 % of the branch circuit, but it doesn't necisarily say that the plug has to be correct size (although common sense would tell you it does) just that the branch circuit is sufficiant.
Thanks for any time you can give me on this.
Matt