A fellow electrician had a service call for no power. Found the 400 Amp 480V breaker at the service (ten feet from the 175 KVA transformer) tripped.
He reset it.
Shortly there after it tripped again.
Another electrician megged the conductors, a dead short. A high pot was then used, dead short. Fault was determined later to be an electrician on a nearby job had cut partially thru the 4" feeder conduit that the 400 A breaker fed and nicked the wire, before it was energized.
The fault blew a hole in the UG PVC
Question: What hazard was there to the electrician who reset the tripped 400 A CB?
Recommended Policy/Procedures?