3 phase question

Status
Not open for further replies.

sticko

Member
Location
nothern virginia
I need to place a cord and cap on a mixer that is three phase 208v. The manual that comes with the mixer requires a "four prong grounding polarized Hubble # 3431-G plug" attached to a SO cord. When I look it up on a NEMA chart, I four blades marked W,X,Y, and Z. I don't see a "G". Is this a grounding plug?
The mixer is on a metal stand. I'm worried about all the metal parts.
 

bth0mas20

Senior Member
Location
Maryland
on the mixer read continuity from the metal stand to the plug on it. That will tell you which one is the ground. then just make sure you use the same prong on the cord cap.
 

Smart $

Esteemed Member
Location
Ohio
3430g_type_p_twi_dia.GIF


http://www.hubbellcatalog.com/wiring/section-b-datasheet.asp?FAM=Locking_Devices&PN=HBL3431GCB
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Looking at the Hubbell Catalog, the 3431 is non-Nema 4pole 4 w 30 amp.
It is not a grounding receptacle or cap.
That said, if you used the "W" as your ground, there would probaly be no problem as long as the plug (male) has no exposed metal..it appears not to...
From a liability standpoint, i would recommend changing to the correct NEDMA configueration.
 