arc fault- does this sound right?

Status
Not open for further replies.

boltneck

Member
vacuum cleaner trips arc fault breaker- no suprise there

there are two receptacles in the hallway, both on the same arc fault breaker
breaker trips instantly when vac is turned on when plugged into one receptacle
works fine plugged into the other one

btw havent been there yet, this comes from the homeowner
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
could be a bad section in the wire. isolate and repeat. You could bypass the run with a spare piece of wire to test.
 

ELA

Senior Member
Occupation
Electrical Test Engineer
What is the distance from each receptacle to the service cabinet(breaker location). Additional wire impedance could be the difference.
 

boltneck

Member
so.. if the breaker is tripping as a result of an arc fault, then it should trip at any receptacle on the circuit. right?
 

boltneck

Member
ok maybe the fog is starting to clear

senario

arc fault ckt with 10 recepts- neutral to ground fault @ mid ckt- ckt will work fine up till the fault

the presence of a neutral to ground fault will not trip an arc fault breaker until a load is applied
 