GrummanWildcat
New member
To provide temporary construction power, the contractor chose to terminate the Grounding Electrode Conductor from building steel to a bolted lug on the outside of a dry transformer case which is through-bolted to a neutral lug on the inside of the case. Both lugs connect to a common bolt separated by the sheet metal housing.
The transformer is a delta/wye 480/120-208 and mounted on a mobile skid with secondary panel attached to the side of the transformer housing. Primary power feeds into a safety switch mounted on the opposite side of housing as the panel. Secondary panel feeds power cords to spider boxes and other job site temporary power.
The question I ponder is if the GEC termination on the outside of the transformer meets the intent of NEC 250.30. NEC Handbook provides two illustrations depicting the GEC terminating at a common lug or buss inside either the transformer or the secondary panel. I would prefer the illustrated scenario with a common lug. However, my job is to determine if the existing by the contractor meets code.
Another variation to consider: If the exterior GEC lug was bolted to the neutral lug inside the transformer, does that change the outcome?