Has anyone ever heard of a requirement to drive TWO ground rods on a new service? I did a service change today and the owner made point to let me know to be sure to put 2 of them about 8 feet apart. New one on me.....
If you do not use a CEE generally you are required to install 2 rods at least 6' apart. the further apart the better. This has been in the code for some time now.
I should add if you can get 25 ohms with one rod then you need not add the other.
our poco requires 2 rods. I didnt know it was in the nec though. I dont have a code book handy, where is it in 250
250.56 Resistance of Rod, Pipe, and Plate Electrodes.
A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(4) through (A)(8). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8 m (6 ft) apart.
FPN: The paralleling efficiency of rods longer than 2.5 m (8 ft) is improved by spacing greater than 1.8 m (6 ft).
I always drive (2) rods in on upgrades & new services, I don't need any call backs from Inspectors.....
DA,
I always drive (2) rods in on upgrades & new services, I don't need any call backs from Inspectors. Few years back I tied my GEC to the water main (copper) and drove in a ground rod below meter socket. Called in inspection, and then get a call back and the inspector wouldn't pass without (2) rods @ meter. His argument was that the town was in the process of upgrading the water mains to plastic, but talking with other folks in town it wasn't true on the water main upgrade. Just cut the loses!
two rods till recently. Boss just stated that since we use uefer ground we no longer have to drive ground rods. Is this correct per code? Or is another local issue. Too many codes not enforced to count around here. Would hate to become an inspector. No one in this town would pass or at least not first try
Around here, they'd happily accept that, if you can prove you have 10+ feet of metal pipe in contact with earth.Since I have 2 electrodes, I only install one ground rod. I have done hundreds of service changes like this and never been corrected by an inspector.