I need a little help on how electrical contractors handle the following:
A 480V 3 phase service is brought in to the middle of a field that has a service disconnect and a panel. A ground rod is driven and the panels neutral is bonded to the ground and then the rod for a separately derived system.
Now about 500 feet away a small motor control panel and convenience outlet is installed, however this motor controller requires 208/120 3 phase. The solution has been determined to install a transformer at the control panel that is over 2kVA to step the voltage down. This situation is set up only to ask a hypothetical question so the answer is not to do it differently.
My understanding of the code is that the neutral must be bonded to the ground that was fed from the service as the transformer is a separately derived source. Also a ground rod would be installed at the output of the transformer and bonded to derived neutral. Also the ground rod will need to be bonded to the services GEC 500 feet back.
1) Is this correct or is there an exception I missed on running the GEC all the way back?
2) Since the conduit coming from the service had 3 phases and a bonding conductor, do I also need to install a GEC too in the conduit or would it go outside the conduit?
3) Couldn't I just make the bonding conductor the same size as the GEC and only install one conductor?
I can't seem to find any code to explain this situation and haven't found anyone to answer it.
A 480V 3 phase service is brought in to the middle of a field that has a service disconnect and a panel. A ground rod is driven and the panels neutral is bonded to the ground and then the rod for a separately derived system.
Now about 500 feet away a small motor control panel and convenience outlet is installed, however this motor controller requires 208/120 3 phase. The solution has been determined to install a transformer at the control panel that is over 2kVA to step the voltage down. This situation is set up only to ask a hypothetical question so the answer is not to do it differently.
My understanding of the code is that the neutral must be bonded to the ground that was fed from the service as the transformer is a separately derived source. Also a ground rod would be installed at the output of the transformer and bonded to derived neutral. Also the ground rod will need to be bonded to the services GEC 500 feet back.
1) Is this correct or is there an exception I missed on running the GEC all the way back?
2) Since the conduit coming from the service had 3 phases and a bonding conductor, do I also need to install a GEC too in the conduit or would it go outside the conduit?
3) Couldn't I just make the bonding conductor the same size as the GEC and only install one conductor?
I can't seem to find any code to explain this situation and haven't found anyone to answer it.