I understand that secondary protection of transformers is not typical. What exactly would be secondary protection of a transformer. I know that 220.21 C allows for taps to be used, allowing us to eliminate secondary protection of a transformer and only provide protection of the secondary conductors.
In my mind the secondary protection would be a cb or set of fuses integrally mounted to a transformer.
Has anyone ever worked on such a transformer.
Here is a question that was brought up in my Master Prep class by the Teacher (which he could not find logical reasoning for), so I'll post it here to see if anyone can shed any light on the subject.
240.21 C 3 stipulates requirements for industrial installations (not over 25 feet long) and 240.21 C 6 stipulates for everywhere else (not over 25 feet long).
Why can you get by with a larger conductor size and overcurrent in other than industrial installations?
One of the stipulations for Industrial installations is that "conditions of maintanence and supervision ensure that only qualified persons service the systems".
I would think that in an "industrial environment" you would be able to get by with smaller ocpd and conductor sizes vs. a commercial store that has no supervision (possibly not even a maintanence person)
In my mind the secondary protection would be a cb or set of fuses integrally mounted to a transformer.
Has anyone ever worked on such a transformer.
Here is a question that was brought up in my Master Prep class by the Teacher (which he could not find logical reasoning for), so I'll post it here to see if anyone can shed any light on the subject.
240.21 C 3 stipulates requirements for industrial installations (not over 25 feet long) and 240.21 C 6 stipulates for everywhere else (not over 25 feet long).
Why can you get by with a larger conductor size and overcurrent in other than industrial installations?
One of the stipulations for Industrial installations is that "conditions of maintanence and supervision ensure that only qualified persons service the systems".
I would think that in an "industrial environment" you would be able to get by with smaller ocpd and conductor sizes vs. a commercial store that has no supervision (possibly not even a maintanence person)