This is really just for fun but that way I read this section is seems you can only
mount a receptacle below the counter in a peninsular if you can't mount one
above it as a pendant type...
210.50 General.
mount a receptacle below the counter in a peninsular if you can't mount one
above it as a pendant type...
210.50 General.
Receptacle outlets shall be installed as
specified in 210.52 through 210.63.
specified in 210.52 through 210.63.
(A) Cord Pendants.
A cord connector that is supplied by a
permanently connected cord pendant shall be considered a
permanently connected cord pendant shall be considered a
receptacle outlet
210.52(C)(5) Receptacle Outlet Location. Receptacle outlets shall
be located above, ...the countertop.....
Exception to (5): To comply with the conditions specified in
(1) or (2), receptacle outlets shall be permitted to be
mounted not more than 300 mm (12 in.) below the countertop.
Receptacles mounted below a countertop in accordance
with this exception shall not be located where the
countertop extends more than 150 mm (6 in.) beyond its
support base.
(2) On island and peninsular countertops where the countertop
is flat across its entire surface (no backsplashes,
dividers, etc.) and there are no means to mount a receptacle
within 500 mm (20 in.) above the countertop,
(1) or (2), receptacle outlets shall be permitted to be
mounted not more than 300 mm (12 in.) below the countertop.
Receptacles mounted below a countertop in accordance
with this exception shall not be located where the
countertop extends more than 150 mm (6 in.) beyond its
support base.
(2) On island and peninsular countertops where the countertop
is flat across its entire surface (no backsplashes,
dividers, etc.) and there are no means to mount a receptacle
within 500 mm (20 in.) above the countertop,