ishium 80439
On a call today that has an obvious problem w/ their feed. I'll spare you all of the details of how I saw single phase voltage go between 70V and 165V depending on what loads were turned on.
Here is the scenario. Single phase 120/240V service There is a pole set w/ meter and main disco at the bottom of the property 300MCM URD runs from the disco about 800' straight to the panel (no disco on the outside of the house, MB panel). The wire is exposed in two places in that run (the HO was able to locate and uncover it).
My question is what is the best way to locate the problem? I remember years ago the POCO using a "thumper" to try to locate a problem by actually trying to disrupt the soil when the fault blew. I certainly don't have one of those in my back pocket. I'm just not familiar with any equipment for this purpose.
And for what it is worth with the equipment we did have (essentially just some Ohm meters) we are fairly confident that there are multiple issues.