i have two seperately derived systems each with four parallel sets of conductors located 200ft from a building.Is it permissible to run the gec to the common grounding point with one of the parallel sets from each "sds",I can't see anything in the code book which allows or disallows this method.
 
i have two seperately derived systems each with four parallel sets of conductors located 200ft from a building.Is it permissible to run the gec to the common grounding point with one of the parallel sets from each "sds",I can't see anything in the code book which allows or disallows this method.

The GEC only needs to run to the closest building steel for each SDS.
 
310.4(C) would not apply to a GEC, but it would apply to an EGC.

Chris

I beg to differ. I don't believe one of the four conduits can have an extra conductor.

(C) Separate Cables or Raceways. Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics. Conductors of one phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor shall not be required to have the same physical characteristics as those of another phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor to achieve balance.
 
I beg to differ. I don't believe one of the four conduits can have an extra conductor.

Good point, I got so involved in the GEC VS EGC thought that I didn't think about the fact that adding a GEC to a single conduit of a parallel installation would still violate 310.4(C).

Chris
 
I guess I may be having a brain cloud here, but if it's a SDS feeding another building, could you not just establish your grounding electrode system at the building wihout a gec from the SDS ?
 
These are standby generators with main breakers,I can establish a GES using re-bar and if necessary a ground rod.However according to 250.30(4)do I need to connect both generator GEC's to the common building electrode system.
 
The reason they are so far away is both for noise and the parking spots the landlord was willing to give up." Twokinsman" you make a good point,but are these generator enclosures considered seperate structures.
 
So in the in the case my re-bar and ground rod would be considered my grounding electrodes? on another note,am I correct in saying that any neutral from my two SDSs and utility cannot be solidly connected as i also see issues with the set-up of the emergency switchgear.
 
had a better look at the job today and found the neutral in the emergency sw gear common to both generators,however the neutral from the utility is isolated through the 4-pole transfer switches.Can I use 250.30(a)(1) exception 1 and bond both systems in the em switch gear leaving the neutrals isolated at the generators even though Im downstream of the ocpd.The em gear consists of 2 main breakers(one for each generator)with a main tie breaker and a solidly bolted neutral.
 
had a better look at the job today and found the neutral in the emergency sw gear common to both generators,however the neutral from the utility is isolated through the 4-pole transfer switches.Can I use 250.30(a)(1) exception 1 and bond both systems in the em switch gear leaving the neutrals isolated at the generators even though Im downstream of the ocpd.The em gear consists of 2 main breakers(one for each generator)with a main tie breaker and a solidly bolted neutral.

MC, article 250.30(A)1 requires the bonding jumper be made at the source up to the first OCPD. If the gensets have OCP, thats where the jumper goes.

The exception that allows the common output to be bonded applies to SDS's the are duel fed. This exception would not apply to your generators.

Rick
 