DSamson
- San Francisco, CA
I'm bidding a job where they are adding an elevator to an existing residence. The residence has 100 Amp service (fuses, not a breaker). The only significant exisiting load is an oven (6.1 kW nameplate). (everything else that makes heat is gas)
Here's all of the data the elevator sub provided:
220V 30A to our disconnect, and
120V 15A to our disconnect
Motor
5 HP, 220V, 60 cycle, single phase, 21 "full load amps", 126 "starting amps", class F insulation
My questions are:
1) What load do I include in my service calculation for this elevator?
2) If the 100A service is still sufficient, does it need to be increased for the locked rotor current of the elevator motor when it starts up? The exsiting main disconnect for the building is fuses.
Looking at Table 430.151(A), I get a locked rotor current of 168A.
From Table 430.110 tells me I need 115% of the full load current for the disconnecting means.
I get a full load current of 28 Amps, from Table 430.148. (Single Phase, AC) It looks like the elevator sub is treating it like a DC motor. His Full Load Amps of 21 seems to come from Table 430.147, 5 HP DC motor.
I'm a little stuck at this point.
Any help with the two questions above would be appreciated.
Thanks
Motor
My questions are:
Thanks