zog
- Charlotte, NC
Coordination ease with other OCPD's - Advantage fuse (when the breakers are molded case - no electronic trip units).
Yeah, same thing I said but you did the double negitive thing.
I think he was meaning that the way a fuse works is to pass all of the current through a very small meltable metal strip, which is MUCH smaller than a set of contacts or a thermal trip element.
If it is a UL489 breaker it will always have an instantaneous protective override function even when the adjustable Instantaneous function has been turned off. This protective function is part of the UL489 standard. Historically manufacturers have never 'reported' or shown this value as a separate part of their time-current curves, although some are now doing so.... you have unintentionally disabled the instantaneous of the device and if it is a UL489 breaker you might now take more than 3 cycles to clear and be putting the protection of the equipment and the breaker in jeopardy.
When a breaker trips, I'll give it one reset try.Fuses get more investivgation.
When a breaker trips,I'll try one restart,then troubleshoot.
Fuses will trip alot sooner then breakers (1/4 to 1/2 second sooner).
The only way to engineer a series combination fuse with any circuit breaker is to be assured that the circuit breaker will remain passive in the first ? cycle of the fault.![]()
Only if there current is high enough for them to enter their current limiting range.I thought fuses opened in the first 1/4 to 1/2 cycle of trip current.
Actually many, if not most, molded case breakers built since the early 60's may begin to open this fast, if the current is high enough.
NFPA 70E 2004 130.6 (K)
Reclosing Circuits After Protective Device Operation.
After a circuit is deenergized by a circuit protective device, the circuit SHALL NOT be manually reenergized until it has been determined that the equipment and circuit can be safely energized.
Note: When it can be determined from the design of the circuit and the
overcurrent devices involved that the automatic operation of a device was
caused by an overload rather than a fault condition, no examination of the circuit
or connected equipment is needed before the circuit is reenergized.
Are there Circuit Breakers that have seperate indication when opened that an overload vs. a short circuit caused the breaker to open?
Are there fuses that have different indication the root cause of being open? (Without cutting it open to see inside)Thanks
That comes from OSHA 1910.334, here is the rest of it.
(b)(2) "Reclosing circuits after protective device operation." After a circuit is deenergized
by a circuit protective device, the circuit protective device, the circuit may not
circuit can be safely energized. The repetitive manual reclosing of circuit breakers
or reenergizing circuits through replaced fuses is prohibited.
Time isn't money when a feed water pump trips a breaker at 1:30 a.m. and it is at a boiler plant at Feb 02.Must get going.I investigate EVERYTHING..time is money and safe is safe.
ZOG,
Thanks for the link and info on breaker retrofits.
I noticed sometthing interesting. I hand typed the text direct from NFPA 70E that indicates that manual reclosure "SHALL NOT" happen until diagnostic methods prove the equipment/cicuit id safe. I do nto have the OSHA document, does it say "may not" or "shall not"?
IMM_Dr.