mark32
Senior Member
- Location
- Currently in NJ
In a multi family dwelling there is a 200a service, after leaving the two meter meter pan, the feeders then feed two 100a main breaker panels. My thinking is you can run a # 4 cu from just one of the panels to the grounding electrode instead of some other arrangements that I've seen/heard. One friend jumped the two panels in the scenario above, I told him he probably didn't have to do that but he said he'd fail if he didn't. I don't agree with this as the feeders in this case contain a grounded conductor sized large enough for the whole 200a service which are of course bonded together at the meter. Does anyone see a problem with this?