mikehughes8
Senior Member
- Location
- NC
I have a 3 Phase / 4 wire service with a feeder connecting to a 208 / 480 (delta / wye) transformer. This Transformer feeds a 100A Panel. Since this is a seperately derived system..am I ok to bond only at the 100A panel and not the source (transformer).
Secondly, a grounding electrode was driven at the source and another electrode was driven at the 100A panel. There is not a bond connecting these electrodes. However, it would seem to me that they are electrically connected via the EGC. With the electrical connection made via the EGC does this qualify as a grounding electrode system and cover me when trying to meet requirements of 250.56? i.e supplemental ground rod when trying to meet 25 ohm requirements.
Thanks...hope that wasn't to confusing.
Secondly, a grounding electrode was driven at the source and another electrode was driven at the 100A panel. There is not a bond connecting these electrodes. However, it would seem to me that they are electrically connected via the EGC. With the electrical connection made via the EGC does this qualify as a grounding electrode system and cover me when trying to meet requirements of 250.56? i.e supplemental ground rod when trying to meet 25 ohm requirements.
Thanks...hope that wasn't to confusing.