Here are some that came up at an IAEI meeting that I spoke about.
1. 210.60. Are TR receptacles required in hotel/motel guest/room suites? What if the hotel/motel guest/room suite had permanent provisions for cooking.
2. 400.7 & 422.16. Other than specific appliances, can fixed or stationary appliances be flexible cord connected? If so, is there a limitation on the size and/or rating, or type of appliance?
3. 422.31, 422.32 & 424.19. What is the difference between an appliance rated over 1/8 HP, a motor driven appliance of more than 2/8 HP, and a heater containing motors rated over 1/8 HP? Is a 1/4 HP air handler considered a motor driven appliance? Is the disconnecting means required to be within sight or only capable of being locked in the open position?
4. 410.74 & 410.120. Can a recessed incandescent luminaire 100W lamp marking be field changed to 60W? If so, is a field follow up required? What lamp watt rating should be used for a lampholder, such as a pendant or keyless luminaire?
5. 400.7 & 410.82. Can a portable luminaire be secured to a bed headboard with the coard passing through and hidden by the headboard? Does it make a difference if the headboard is secured to the bed or the wall? Can a 100W incandescent luminaire be mounted on a fixed headboard? Can a 100W incandescent luminaire wired with 18 AWG SPT-2 cord include a receptacle outlet with a marked rating to limit the load to 3.5A total?
6. 110.3(A), 408.3(G) & 312.6. Where conductors enter a switchboard, and the wire bending space appears to be insufficient, is there a code violation if the requirements of 312.6 are met? How do we determine wire bending space where the raceway size is known but the conductor size is unknown? Does parallel apply to the raceways of the conductors?
7. There are 249 instances of the term "Physical damage" in the NEC. The term is not defined in the NEC. What is the intent of the term "physical Damage"? How do we determine if electrical equipment is subject to "physical damage"?
8. 110.16. Dows the field marking requirement apply only to equipment
inside the occupancy only? Does the field marking requirement apply to equipment
outside the occupancy too?
The summary was this.
- the code contains many gray areas
- identify the gray areas
- clarify the intent
- use reason, logic, and common sense
- submit code change proposals
And I haven't done this much typing all month:grin:
If all else fails see Charlies' rule.