Why does 690.62(B)(2) limit total breaker sum for solar, but no limit for non-solar?

Status
Not open for further replies.

donw

Senior Member
Location
Arizona
690.64 (B)(2) limits the sum of the ampere ratings of OC devices on a bus to the rating of the bus (with the exception of +20% for dwellings). This makes retrofitting for solar quite difficult and expensive in many instances. Why does this rule exist in the first place? We routinely design systems where the sum of all the OC devices add to more than the rating of the bus, for example, a main-lug switchgear bus may be rated for 1000A but have 1200A worth of breakers. We simply show that the sum of all loads (and 125% of continuous loads) is less than 1000A. Why not the same for solar systems?
 
In normal systems the line side device limits the maximum current that can flow on the panel bus. In the case of solar, you have two "line side" OCPDs that can supply current to the panel bus and you could overload the bus. The code rule permits a 20% overload of the bus. Note that the 20% applies to all occupancies in the 2008 code.
 
Thanks, Don. I guess in the case of a service entrance equipment, then it's the utility's OC device. That's great news about the 2008 Code.
 
Thanks, Don. I guess in the case of a service entrance equipment, then it's the utility's OC device. That's great news about the 2008 Code.
It would be the service OCPD if you are conecting the solar to the service panel. The utility OCPD would never enter into this issue.
 
Don, that is what I'm talking about - a service entrance with main-lugs-only. We often have OC devices totaling over the rating of the equipment bus, but the calculations show the load will be less than the bus, so it's okay. But with solar added??
 
Don, that is what I'm talking about - a service entrance with main-lugs-only. We often have OC devices totaling over the rating of the equipment bus, but the calculations show the load will be less than the bus, so it's okay. But with solar added??
Sorry, I didn't really understand your question. In that case, I don't see any rule as to the size of the OCPD. The rule in 690.64(B)(2) only applies to solar connections on the load side of the service disconnect. 690.(B)(1) applies where the output of the solar system in connected on the line side of the service disconnect. The rule only refers you to 230.82(6) but gives no guidance as to the size of the OCPDs.
 
I hadn't thought about it being on the line side of the service disconnect(s), but I guess it really is. The other disconnects are the service disconnects, and the one connected to the solar equipment is really on the line side. Interesting.
 
Wait a minute, I don't think that's right. What I'm talking about is a main-lug-only service equipment with multiple (6 or less) disconnects/OC devices. Lets say 5 are service disconnects, and one is the solar disconnect. They still combine on the load side of the disconnects.
 
The panel bus is on the line side of the service disconnects so the solar system connection is on the line side of the service disconnects. With a MLO panel the breakers are the service disconnects and the load side of the breaker is the load side of the service disconnect.
 
I'm not sure if I'm doing this according to the rules so please bear with me. I understand 690.64 (B)(2) limits the sum of the ampere ratings of OC devices on a bus that are feeding the bus. I would think the 5 OCPDs on the bus with the solar OCPD would not count because they are not feeding the bus they are on.
 
PV with main-lug-only service equipment with multiple (6 or less) disconnects

PV with main-lug-only service equipment with multiple (6 or less) disconnects

If you have main-lug-only service equipment with multiple (6 or less) disconnects, the PV breaker can be up to the rating of the bus. PV breaker must be on the opposite end of the bus from the utility feed.
 
If you have main-lug-only service equipment with multiple (6 or less) disconnects, the PV breaker can be up to the rating of the bus. PV breaker must be on the opposite end of the bus from the utility feed.
For installations where the PV breaker is on the line side of the service disconnect(s), there is no code rule that says the PV breaker must be on the opposite end of the bus. That rule only applies to PV breakers that are installed on the load side of a service disconnect.
 