Karl H
- San Diego,CA
What ART. states that I can make a splice in a ATS if of the same power source?
There is none, but there is nothing that says you can not. :smile:
Defensive code art. might be 312.8.
See 350.30 for the LT.
Karl, I know there's more to the story than a splice ?
The burden of proof of non-compliance is upon the inspector.Yeah, 312.8 is what I quoted. But, as Bob said, "It dosen't say you can, and it dosen't say you can't."![]()
Yeah, 312.8 is what I quoted. But, as Bob said, "It dosen't say you can,and
It's a switch, unless the AHJ can make a stand on head dissipation, don't see where he has a leg to stand on. Call the manufacturer of the ATS and have them fax a copy to you of something saying you can do this {makes it a 110.3(B)}.
I always assumed that if it were just splicing the 75% is however much will fit within reason into the box/area that remains. Sounds like the AHJ is is inspecting on how he feels, not what the law says.
Part 2 is it worth if it you win the battle, but lose a war? Battles have to be chosen carefully against future activities...
Does it say in the spec or on the drawings, No splices in the ATS?
Karl, What exactly is the splice ? Is it 2 or 3 conductors ? What size wire ? what is it feeding ?