N normbac Senior Member May 13, 2009 #1 Inspector wants torque certs on breakers and neutral buss its a 200 amp panel on a rec center at an apartment complex, was wondering if this is a standard request. TIA
Inspector wants torque certs on breakers and neutral buss its a 200 amp panel on a rec center at an apartment complex, was wondering if this is a standard request. TIA
Buck Parrish Senior Member Location NC & IN May 13, 2009 #2 normbac said: was wondering if this is a standard request. TIA Click to expand... No,,,,,,,,,,,,,,,,,,,,,,,,,,,
normbac said: was wondering if this is a standard request. TIA Click to expand... No,,,,,,,,,,,,,,,,,,,,,,,,,,,
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 13, 2009 #3 Not standard at all.
electricalperson Senior Member Location massachusetts May 13, 2009 #4 the nec does require us to torque down and follow the UL listing. maybe he was trying to follow 110.3B and the FPN of 110.14 by getting proof
the nec does require us to torque down and follow the UL listing. maybe he was trying to follow 110.3B and the FPN of 110.14 by getting proof